I thought I was having a senior moment, but then found it.  Section
14.4.4.5 (2) (02 edition) says to NOT include tie-in drain piping in
hydraulic calcs.

Ed Kramer
Littleton, CO


>
>If it is a drain line, you would include it in the hydraulic calculations
>WHY??
>
>
>
>Jeff Hewitt, PE, SET, SFPE (Prof. Member)
>Corporate Engineer
>Bi-State Fire Protection Corporation
>636-946-0011