There is a flaw in your reasoning. IF 14.4.4.5 was a connection from different pipes to the drain without any interconnection, how could it impact the hydraulic calculation since the flow would only be out of the system to the drain?

The tie-in drain is used only 8.15.2.5.2.4 and 8.15.2.5.3.4 (which provides the basic definition of interconnection branch lines). Then chap 14 tells use tie-ins are not to be part of the hydraulic calculation which is conservative since only a gain (small as it might be) would be seen.

It is intended to minimize their use IF POSSIBLE but the explicit text in the drain section trumps the general text on forbidding grids in dry pipe systems.

Roland

On Jun 28, 2007, at 8:59 AM, [EMAIL PROTECTED] wrote:

Easy. 8.15.2.5.3.4 specifically addresses multiple adjacent trapped branch pipes and 14.4.4.5 does not. 14.4.4.5 is general and is not addressing the connecting of the ends of branch lines. 14.4.4.5 is addressing a drain
that connects to a pipe in the system and drains to an outlet without
connection to other piping in the system.

Thank You

Rahe Loftin, P.E.