Granted the clouds may not allow a sprinkler to "effectively extinguish a fire below such an assembly" but when did extinguishment become a requirement and how will a sprinkler installed in a 4x4 panel prevent diversion of combustion gasses?
We call them feel good sprinklers, they won't go off because there is no heat collection but they make the AHJ's and engineers happy. Ron Fletcher Aero Automatic Phoenix, AZ -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Wednesday, August 15, 2007 1:07 PM To: [email protected] Subject: RE: Ceiling Clouds throughout Band / Choir Room Even though the clouds are 3'-11 and technically under the 4'-0 rule (8.6.5.3.3) with only 1'-0 up to 4'-0 between the panels what will the effective spray pattern be from heads installed at the underside of the roof deck? If you had 4 panels with only 12" between the panels you've essentially got a 16x16 ft obstruction and would you really expect sprinklers to effectively extinguish a fire below such an assembly? Also while we're discussing obstruction to water spray, what about diversion of combustion gasses to sprinklers not near the actual fire source? Is this considered? I don't know if the 3'-11 measurement is off the actual cloud/ a shop drawing or off of an architectural drawing. If you're scaling something off a cad drawing I wouldn't try to call it that close, chances are it'll be 48"+. What did Dirty Harry say, "do ya feel lucky?" .................. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.lg.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Rapid Fire - Bismarck Sent: Wednesday, August 15, 2007 3:18 PM To: [email protected] Subject: RE: Ceiling Clouds throughout Band / Choir Room I appreciate all's input on the matter. (Taking 8.6.5.2.1.4 into consideration) Though I'm 'nickel and dime'ing the situation - measurement of the panels are 3'-11" square. Whew! Under 4'!! Seriously though - in a room measuring 48'-9" square, there's 56 of these panels! ½" have a convex contour... the others - concave. I'll be making a call to the respective A.H.J. and get his take on it. Thanks again! No virus found in this outgoing message. Checked by AVG Free Edition. Version: 7.5.476 / Virus Database: 269.11.19/953 - Release Date: 8/14/2007 5:19 PM _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)