George,
Control it is.

Bob

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George Church
Sent: Wednesday, August 15, 2007 4:02 PM
To: [email protected]
Subject: RE: Ceiling Clouds throughout Band / Choir Room

Wouldn't hurt to point out the dilemma of "it meets the code but the
effectiveness is cut substantially; my contractual obligation is met by
meeting the code; if you would like us to provide protection in excess of
the code and drop heads below the panels, we'll develop a COR for your
consideration.

Their response, or lack of it, may spare some legal defense costs in the
future; perhaps ensure the future of Rapid Fire as a "going concern".

One thing is for sure- it would be prudent to have acknowledgement that 
a) you met code with just uprights
b) you brought the code vrs reality to the attention

Believe me when I say you do NOT want to be debating the acceptability of
it, or the code compliance issue, in a courtroom years from now as a
precedent to apportioning % of blame and share of resultant damages.

We've had incidents where the insurance adjuster, after getting a copy of
our dog and pony letter wherein the owner's rep has signed off acknowledging
responsibility for the system including ITM and protection of wet system
from freezing, has called us and said "Thanks for making my job easy".
That letter and the dog and pony show has been MANDATORY standard operating
procedure on EVERY job we do for years. As Russ L says in his #25 seminar,
if you do a lot of work or if you do it for awhile, it's not IF you have a
fire (freezeup, incident) in one of your buildings, its WHEN you have a....

Think of it as legal preventative maintenance. Far easier now than later,
and heck- maybe you'll get a few extra bucks and install a better system for
the time to write one letter or email.

Glc

Ps I believe the wording is CONTROL the fire, vrs suppression mode (ESFR).

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bob Knight
Sent: Wednesday, August 15, 2007 5:47 PM
To: [email protected]
Subject: RE: Ceiling Clouds throughout Band / Choir Room

Craig,
I agreed with you on the quantity and closeness of the panels, I was merely
pointing out the fact that an object is not an obstruction just because it
is 48" wide.  It's not an obstruction until it exceeds the 48" threshold.
As far as are sprinklers required; it will depend on the actual layout of
the panels.  It may be that there are areas were it would be advisable to
place pendants in the panels, while there may be other areas where this can
be avoided.  This is why I'm not sold either way.  The layout will dictate
where sprinklers will be required.  As Garth mentioned, I think it was
Garth, the fire sprinklers are designed to contain not suppress the fire.
While we all want to see every fire suppressed, this is not the intent.  It
is an excellent bonus though that most fires are suppressed by sprinklers,
and I agree that we need to be diligent in our designs so as not to create
systems that will be destined to fail.

Bob K


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG Free Edition. 
Version: 7.5.476 / Virus Database: 269.11.17/951 - Release Date: 8/13/2007
10:15 AM
 

No virus found in this outgoing message.
Checked by AVG Free Edition. 
Version: 7.5.476 / Virus Database: 269.11.17/951 - Release Date: 8/13/2007
10:15 AM
 