I chime in because there have been some misconceptions.

First off "Only structural members have to be treated as obstructions". This is not applicable because multiple adjacent obstructions are not intended to be looked at individually but by what they do as a group. Since the clouds affect adjacent sprinklers, they are considered CONTINUOUS. There was a case where a crafty architect didn't want to see the sprinklers so he located a light directly below and close to EVERY sprinkler. It meet the literal letter IF one ignores the fact that continuous means something that affects not one but adjacent sprinklers. Soooooo, the TC wrote A.8.6.5.2.1.4 "It is not the intent of this section to permit the use of fixtures and architectural features or treatments to conceal, obscure, or otherwise obstruct sprinkler discharge. The exception should be applied in accordance with the performance objectives of 8.6.5.1."

Secondly: It gets sticky once you go beyond 36 inches below the deflector. In this case you have approximately 3"0" between the deck and panels. You more than likely less than 36 inches below the deflector. If you were greater than 36 inches then you have to discuss GROUPING of the obstructions with the AHJ and whether they are to be treated individually or together. WHat do you think the outcome will be? If they were all 4 ft apart and further down, then we would have something that I would debate especially since the fuel load is rather light.

I disagree that a 3'11" square would not capture enough heat activate to activate a sprinkler. At least I would have a difficult time arguing that the results of tests showing a SMALL heat collector negatively affects the plume should be extrapolated to a 3'11" square.

As such, sprinklers are required throughout the real ceiling, ie the deck(I've seen plenty where they are just below the clouds) and below the obstructions.

SInce I am rendering an option, I need to state as a member of NFPA 13 that this is not an interpretation by NFPA or any of its technical committees (though the annex text is rather explicit).

Roland

On Aug 15, 2007, at 11:21 AM, Rapid Fire - Bismarck wrote:

I know the ceiling cloud issue has been beaten to death, and I apologize for
re-scratching an irritated wound...

Scenario:
Band - Choir room(s) with 4' x 4' acoustical dampening-style clouds littered throughout the room w/ space created between the panels ranging from 1'-0" ~ 4'-0" 'open' space. Structure above is steel joist - approximately 3'-0" clearance from top of panel to bottom of decking. I do not believe these panels fall under the "Drop-out Ceiling" section... therefore, I'm wondering if my spacing would be to place deflector within 6" of the deck and place
around / near the openings created between the panels.  Any thoughts,
previous experiences? Knowledge from the forum is always appreciated!!

Chuck

No virus found in this outgoing message.
Checked by AVG Free Edition.
Version: 7.5.476 / Virus Database: 269.11.19/953 - Release Date: 8/14/2007
5:19 PM

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:Sprinklerforum- [EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to