It may not extinguish but it should definitely contain, notify responders
(through the alarm) and prevent damage to the structure from uncontrolled
heat gain.

Garth

----- Original Message ----- 
From: <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Wednesday, August 15, 2007 3:07 PM
Subject: RE: Ceiling Clouds throughout Band / Choir Room


Even though the clouds are 3'-11 and technically under the 4'-0 rule
(8.6.5.3.3) with only 1'-0 up to 4'-0 between the panels what will the
effective spray pattern be from heads installed at the underside of the roof
deck? If you had 4 panels with only 12" between the panels you've
essentially got a 16x16 ft obstruction and would you really expect
sprinklers to effectively extinguish a fire below such an assembly?  Also
while we're discussing obstruction to water spray, what about diversion of
combustion gasses to sprinklers not near the actual fire source?  Is this
considered?

I don't know if the 3'-11 measurement is off the actual cloud/ a shop
drawing or off of an architectural drawing.  If you're scaling something off
a cad drawing I wouldn't try to call it that close, chances are it'll be
48"+.  What did Dirty Harry say,  "do ya feel lucky?" ..................


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Rapid Fire -
Bismarck
Sent: Wednesday, August 15, 2007 3:18 PM
To: [email protected]
Subject: RE: Ceiling Clouds throughout Band / Choir Room

I appreciate all's input on the matter.  (Taking 8.6.5.2.1.4 into
consideration) Though I'm 'nickel and dime'ing the situation - measurement
of the panels are 3'-11" square.  Whew!  Under 4'!!  Seriously though - in a
room measuring 48'-9" square, there's 56 of these panels!  ½" have a convex
contour... the others - concave.
I'll be making a call to the respective A.H.J. and get his take on it.

Thanks again!

No virus found in this outgoing message.
Checked by AVG Free Edition.
Version: 7.5.476 / Virus Database: 269.11.19/953 - Release Date: 8/14/2007
5:19 PM

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to