And just when I'd say I'd throw in the heads... along comes Ron w/ a reality
check... damn problematic situations...

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron
Sent: Wednesday, August 15, 2007 5:26 PM
To: [email protected]
Subject: RE: Ceiling Clouds throughout Band / Choir Room

George, I'm usually with you on your answers but not this time.

Reality - Submit the COR, get the extra, install the heads in the
clouds. Fire in band room, sprinklers installed in clouds fail to
activate for lack of heat collection. Sprinklers at roof deck control
fire until arrival of FD. School sues FP contractor for selling extra
work that was not required by code and did not work as advertised.

That's why I call them "feel good sprinklers". They look good but don't
work.

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George
Church
Sent: Wednesday, August 15, 2007 3:02 PM
To: [email protected]
Subject: RE: Ceiling Clouds throughout Band / Choir Room

Wouldn't hurt to point out the dilemma of "it meets the code but the
effectiveness is cut substantially; my contractual obligation is met by
meeting the code; if you would like us to provide protection in excess
of the code and drop heads below the panels, we'll develop a COR for
your consideration.

Their response, or lack of it, may spare some legal defense costs in the
future; perhaps ensure the future of Rapid Fire as a "going concern".

One thing is for sure- it would be prudent to have acknowledgement that
a) you met code with just uprights
b) you brought the code vrs reality to the attention

Believe me when I say you do NOT want to be debating the acceptability
of it, or the code compliance issue, in a courtroom years from now as a
precedent to apportioning % of blame and share of resultant damages.

We've had incidents where the insurance adjuster, after getting a copy
of our dog and pony letter wherein the owner's rep has signed off
acknowledging responsibility for the system including ITM and protection
of wet system from freezing, has called us and said "Thanks for making
my job easy".
That letter and the dog and pony show has been MANDATORY standard
operating procedure on EVERY job we do for years. As Russ L says in his
#25 seminar, if you do a lot of work or if you do it for awhile, it's
not IF you have a fire (freezeup, incident) in one of your buildings,
its WHEN you have a....

Think of it as legal preventative maintenance. Far easier now than
later, and heck- maybe you'll get a few extra bucks and install a better
system for the time to write one letter or email.

Glc

Ps I believe the wording is CONTROL the fire, vrs suppression mode
(ESFR).

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bob
Knight
Sent: Wednesday, August 15, 2007 5:47 PM
To: [email protected]
Subject: RE: Ceiling Clouds throughout Band / Choir Room

Craig,
I agreed with you on the quantity and closeness of the panels, I was
merely pointing out the fact that an object is not an obstruction just
because it is 48" wide.  It's not an obstruction until it exceeds the
48" threshold.
As far as are sprinklers required; it will depend on the actual layout
of the panels.  It may be that there are areas were it would be
advisable to place pendants in the panels, while there may be other
areas where this can be avoided.  This is why I'm not sold either way.
The layout will dictate where sprinklers will be required.  As Garth
mentioned, I think it was Garth, the fire sprinklers are designed to
contain not suppress the fire.
While we all want to see every fire suppressed, this is not the intent.
It is an excellent bonus though that most fires are suppressed by
sprinklers, and I agree that we need to be diligent in our designs so as
not to create systems that will be destined to fail.

Bob K


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG Free Edition. 
Version: 7.5.476 / Virus Database: 269.11.19/953 - Release Date: 8/14/2007
5:19 PM
 

No virus found in this outgoing message.
Checked by AVG Free Edition. 
Version: 7.5.476 / Virus Database: 269.11.19/953 - Release Date: 8/14/2007
5:19 PM
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to