Is this a rated wall?  If so the building code classifies the rated walls as 
either a partition wall, fire barrier or fire wall.  Pretty clear def. (if 
you're in IBC land)
Sent from my BlackBerry® wireless device

-----Original Message-----
From: Bob Knight <[EMAIL PROTECTED]>

Date: Fri, 17 Aug 2007 17:22:25 
To:"[email protected]" <[email protected]>
Subject: Barrier / Partition Definition


Does anyone have a good definition for what 11.1.2 means by "Barrier" or
"Partition" (NFPA 13 2002 ed).  I have a friend who has an AHJ telling him
that an 8" concrete full height wall with two door openings in it does not
qualify. My understanding of this is that this is a perfectly acceptable
barrier since the purpose of the barrier is to prevent fusing of the
sprinklers from one area to another.  The reason the question arises is that
this AHJ wants to extend a new .55 / 2500 sf area through the concrete wall
and into an existing .2 / 1500 sf system. Without being too obvious, the
original system has no possibility of providing this density, let alone the
proper spacing of sprinklers. Anyway, any help will be appreciated.

Thank you,

Bob Knight, CET
(208) 495-2057
[EMAIL PROTECTED]
www.firebyknight.com


No virus found in this outgoing message.
Checked by AVG Free Edition.
Version: 7.5.484 / Virus Database: 269.12.0/957 - Release Date: 8/16/2007
1:46 PM


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to