Vance,
Thank you.  When I spoke to this friend, Jerry, the EFSR example is the very
same one that we both mentioned.  Also, all of your talking points are the
same ones that we spoke about.  I appreciate the input, and as well the
validation as to what we had spoken about.

Bob Knight

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ray Vance
Sent: Monday, August 20, 2007 6:23 AM
To: [email protected]
Subject: RE: Barrier / Partition Definition

Bob,

The language is such that the standard clarifies the PURPOSE of the
barrier, ie "barrier or partition capable of trapping heat" in its
requirement to provide such a barrier or partition.
If you go further into this type of requirement in the NFPA standards,
you could also correlate it to the separation required between ESFR
systems and standard response systems, the only requirement for the
"barrier or partition" being a draft curtain, if there are no walls or
other separations in place.

Both requirements are to keep a lower hazard area from operating
prematurely adjacent to a higher hazard area, thereby robbing the higher
hazard area of its intended minimum water supply.

Sometimes the use of a word such as "barrier" or "partition" is taken
too literally, when all that is intended ( if you read ALL the language
of the standard and not just picking out a few words) is to create a
mininal separation (not a fire or other rated assembly) so the sprinkler
system operates in the most efficient manner.

In this case it doesn't appear to be a proper application of the
language of 11.1.2, in that the wall WILL provide the barrier or
partition required by the intent of the standard, ie IS CAPABLE OF
TRAPPING HEAT!

Top of the day to you all!

Ray Vance
Chief Engineering Tech.
Wayne Automatic Fire Sprinklers, Inc.
(407) 656-3030
www.waynefire.com





-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bob
Knight
Sent: Friday, August 17, 2007 5:22 PM
To: [email protected]
Subject: Barrier / Partition Definition

Does anyone have a good definition for what 11.1.2 means by "Barrier" or
"Partition" (NFPA 13 2002 ed).  I have a friend who has an AHJ telling
him that an 8" concrete full height wall with two door openings in it
does not qualify. My understanding of this is that this is a perfectly
acceptable barrier since the purpose of the barrier is to prevent fusing
of the sprinklers from one area to another.  The reason the question
arises is that this AHJ wants to extend a new .55 / 2500 sf area through
the concrete wall and into an existing .2 / 1500 sf system. Without
being too obvious, the original system has no possibility of providing
this density, let alone the proper spacing of sprinklers. Anyway, any
help will be appreciated.

Thank you,

Bob Knight, CET
(208) 495-2057
[EMAIL PROTECTED]
www.firebyknight.com


No virus found in this outgoing message.
Checked by AVG Free Edition. 
Version: 7.5.484 / Virus Database: 269.12.0/957 - Release Date:
8/16/2007
1:46 PM
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Wayne Automatic Fire Sprinklers, Inc.
2006 Inductee into "The Players Hall of Fame"
at The Great Games of Business
Wayne Automatic Fire Sprinklers, Inc. "Best Places to Work"
Rated #1 in 2006
Large Business Category
by Orlando Business Journal
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG Free Edition. 
Version: 7.5.484 / Virus Database: 269.12.1/962 - Release Date: 8/20/2007
1:08 PM
 

No virus found in this outgoing message.
Checked by AVG Free Edition. 
Version: 7.5.484 / Virus Database: 269.12.1/962 - Release Date: 8/20/2007
1:08 PM
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to