The definition of fire wall, fire partition, fire barrier comes from the
building code.  If using the IBC see Chapter 7.   Depending on the
occupancies and the level of sprinkler protection you may or may not be
required to provide one of the three.  Each one has slightly different
characteristics as defined.  The Fire Wall being the most stringent
where the assembly extends from the slab to or even through the roof and
is capable of maintaining its structural integrity even if the building
on either or both sides would collapse.  A fire partition  is a physical
separation designed with fire resistant materials whose purpose is to
prevent the spread of fire from one area to the next.  A fire partition
is not "rated".   The fire barrier is a rated assembly but not to the
extent of the Fire Wall.  All have protected openings as well.

The wall, barrier and partition are designed to protect one occupancy
from fire spread from an adjacent occupancy.  They have a different
purpose than a draft curtain.

As far as the scenario described, if the openings are not protected with
either fire doors or shutters or an accepted (by the AHJ) water spray
curtain, then by definition it does not qualify as a Code defined
separation. It would provide no real separation and his assessment of
requiring the extension of the higher density into the lesser density
protected area would be correct.

So the question is, do the openings have any kind of automatic closures,
is the wall rated, is the wall required to be rated or just one of the
lesser assemblies?  Still a few outstanding questions needing to be
answered in order to make a definitive determination.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bob
Knight
Sent: Friday, August 17, 2007 5:22 PM
To: [email protected]
Subject: Barrier / Partition Definition

Does anyone have a good definition for what 11.1.2 means by "Barrier" or
"Partition" (NFPA 13 2002 ed).  I have a friend who has an AHJ telling
him that an 8" concrete full height wall with two door openings in it
does not qualify. My understanding of this is that this is a perfectly
acceptable barrier since the purpose of the barrier is to prevent fusing
of the sprinklers from one area to another.  The reason the question
arises is that this AHJ wants to extend a new .55 / 2500 sf area through
the concrete wall and into an existing .2 / 1500 sf system. Without
being too obvious, the original system has no possibility of providing
this density, let alone the proper spacing of sprinklers. Anyway, any
help will be appreciated.

Thank you,

Bob Knight, CET
(208) 495-2057
[EMAIL PROTECTED]
www.firebyknight.com


No virus found in this outgoing message.
Checked by AVG Free Edition. 
Version: 7.5.484 / Virus Database: 269.12.0/957 - Release Date:
8/16/2007
1:46 PM
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to