13D requires all heads to be residential type, and a 2 head design, whereas
13R differentiates areas outside he dwelling which require non-residential
heads and designed as per NFPA 13. That is where the problem lies. There is
no difficulty making a 4 head design work with a 2" UG, (assuming it is not
too long, of course). The problem is how would you design mech. rooms,
generally over 2000 s.f. and other similar areas outside the dwelling unit,
with a 2" UG, if the applicable code is 13R? The difference in 13D and 13R
is not only the 2 head vs. 4 head.

Tony 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton
Sent: August 20, 2007 11:48 AM
To: [email protected]
Subject: RE: large single family houses

Why do you need a 4" UG for 13R?  We do them on 2 and 2-1/2" UG's all
the time, including combined services with a domestic allowance taken
for fixture count at the common supply point.   Is this to be a
dedicated 2" fire service or a combined line?

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva
Sent: Monday, August 20, 2007 9:56 AM
To: [email protected]
Subject: RE: large single family houses

I had this question when designing a 32,000 sq.ft. home. The mech.
consultant specified 13D. I recommended 13 or at least 13R. They settled
for
13R. But by this time a 2" underground was already installed. They
wouldn't
give me the 4" underground I needed for designing to 13R. Finally it was
designed to 13D for a two head calc and agreed (at my insistence) to
provide
a pump for a 4 head calc. 

I can't believe they had money for providing a CO2 system for the elect.
room but refused to upgrade the system to 13R.

Tony  

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams
- work
Sent: August 20, 2007 10:09 AM
To: [email protected]
Subject: large single family houses

What's the latest poop on protecting large single-family residences? 
It doesn't seem that 13D would be appropriate for the structure, but 
I don't see anything in any of my Codes that would modify it.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to