I second Jim Robert's motion. To answer your question, though, I don't consider computer equipment as being susceptible to deep seated fires. On the other hand, I have seen pallets of paper, overflowing bins and office furniture in such places.. [EMAIL PROTECTED] Ed Vining 4819 John Muir Rd Martinez CA 94553 925-228-8792
----- Original Message ---- From: "[EMAIL PROTECTED]" <[EMAIL PROTECTED]> To: [email protected] Sent: Thursday, August 23, 2007 7:49:55 AM Subject: Re: Carbon Dioxide System Discharge Time Reza: I would not recommend a CO2 system as it is potentially too dangerous. I would consider a clean agent sytem per NFPA 2001. Hopefully, this is only a back-up to a wet pipe system, which is still my favorite. Regards, James L.(Jim) Roberts, PE, SET Fluor Corporation 100 Fluor Daniel Drive - C104F Greenville, SC 29607 864.281.5149 864.281.4916(Fax) Reza Esmaeili <[EMAIL PROTECTED]> Sent by: To [EMAIL PROTECTED] [email protected] prinkler.org cc 08/23/2007 10:18 AM Please respond to Subject sprinklerforum Carbon Dioxide System Discharge Time Hi all, For designing a total flooding high pressure carbon dioxide system in a 3,500 cubic feet computer room with electrical equipment and cable runs, I have specified my room as "Dry electrical hazard" with flooding factor of 0.083 lb/cubic.feet and 50% design concentration according to NFPA-12. My questions are as below: 1)- Is a computer room fire a deep seated fire? 2)- NFPA 12 states that "For deep-seated fires, the design concentration shall be achieved within 7 minutes, but the rate shall be not less than that required to develop a concentration of 30 percent in 2 minutes." Is it a problem if the total discharge time would be only 1 minute for this case? Many thanks for your help in advance. Reza --------------------------------- Pinpoint customers who are looking for what you sell. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) ------------------------------------------------------------ The information transmitted is intended only for the person or entity to which it is addressed and may contain proprietary, business-confidential and/or privileged material. If you are not the intended recipient of this message you are hereby notified that any use, review, retransmission, dissemination, distribution, reproduction or any action taken in reliance upon this message is prohibited. If you received this in error, please contact the sender and delete the material from any computer. Any views expressed in this message are those of the individual sender and may not necessarily reflect the views of the company. ------------------------------------------------------------ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)