Good Morning Forum Gurus,

 

I have a question that I think I know the answer to but, don't want to
accept it yet, so I'd like to get some outside opinions.  

 

Here's what happened.  We just completed a small remodel project on a wet,
pond fed system.  We only had to alter the office area of a storage
facility.  It was around two dozen heads in all.  A dozen heads on the first
floor, and a dozen heads on the second floor.  The existing system DID NOT
have return bends to feed these pendent heads.  On the first floor we simply
re-swung the arm-overs to accommodate a new ceiling layout.  On the second
floor we added three new branchlines, each on an eight inch riser nipple,
and kept the existing pipe schedule.  I can't remember if we tore out the
existing branchlines, or if we just left them above the ceiling (I don't
hear much about projects once they leave my office).  I had never designed a
pond-fed system before, and I simply overlooked return bends.  

 

We have completely finished this project.  Yesterday we received a fax
pointing out our error that return bends were not installed, and telling us
to fix them.

 

So having said all that (clear as mud right?), do we need the return bends?
Is it our responsibility to correct that mistake on a previously accepted
system?  If we had done a lot of changes, then I think it would be
different; but we just relocated the heads that were already there.  Are
there any other exceptions other than 8.14.18.3 and 8.14.18.4 of the '02 ED.
(8.15.18.3 and 8.15.18.4 of the '07 ED.)?  Basically do we have any other
options, other than taking the loss and fixing the arm-overs?  If you do
think we have to fix them, do you think we should have fix both floors or
just second?

 

Thanks for the help all.

 

Jimmy Waite  (FNG)

Burtell Fire Protection, Inc.

[EMAIL PROTECTED]

(406) 652-7697

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to