Jimmy, 2 more cents. The NFPA 25 reference doesn't hold water since NFPA IT&M by definition and as stated ad nauseum on this forum is a functional inspection and test and a preventative maintenance standard. That said, since you modified a portion of a sub-standard existing system it was incumbent on you (your company), as an NFPA 13 specialist, to at least correct those drops that you altered and as a matter of due dilligence to bring the issue to the owner's attention.
On 8/29/07, Jimmy Waite <[EMAIL PROTECTED]> wrote: > Thanks for the responses. Those were the answers that I was expecting. > We're going to go ahead and fix the arm-overs > > > > Jimmy Waite > > Burtell Fire Protection, Inc. > > [EMAIL PROTECTED] > > (406) 652-7697 > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)