I'd agree to change the drops to return bends IF you SHOULD HAVE KNOWN the
system was fed by a non-potable water supply. If you weren't advised, and it
wasn't obvious, then it could be an extra.

AND I'd give them a proposal to fix ALL the others, at your going, I assume
profitable, T&M rate, and note that the balance of the heads need to be
changed. I'd also inform the AHJ of the existing deficiency IN WRITING now
that you're aware of it.

glc 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman
Sent: Wednesday, August 29, 2007 3:47 PM
To: [email protected]
Subject: Re: Return Bends

Jimmy,

2 more cents. The NFPA 25 reference doesn't hold water since NFPA IT&M
by definition and as stated ad nauseum on this forum is a functional
inspection and test and a preventative maintenance standard. That
said, since you modified a portion of a sub-standard existing system
it was incumbent on you (your company), as an NFPA 13 specialist, to
at least correct those drops that you altered and as a matter of due
dilligence to bring the issue to the owner's attention.

On 8/29/07, Jimmy Waite <[EMAIL PROTECTED]> wrote:
> Thanks for the responses.  Those were the answers that I was expecting.
> We're going to go ahead and fix the arm-overs
>
>
>
> Jimmy Waite
>
> Burtell Fire Protection, Inc.
>
> [EMAIL PROTECTED]
>
> (406) 652-7697
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to