Hello Garth,

Tuesday, September 11, 2007, 8:53:55 PM, you wrote:

GWW> Question - There are several dormitory clusters served by a single on-site
GWW> 6" underground piping system.  The underground enters a building, passes
GWW> through a backflow preventer, and then exits the building and serves the
GWW> several clusters and the site hydrants around the clusters.  Each cluster
GWW> consists of three to four structures which range from two to four stories 
in
GWW> height.  There are three clusters arranged around cul-de-sacs with an
GWW> elevation difference between the upermost cluster and the lowest cluster of
GWW> about 35 feet.  Each structure has an underground gate valve with a curb 
box
GWW> (although the location of several of these could not be confirmed), a
GWW> combination drain/test valve - piped with a piece of pipe shorter than a
GWW> foot through the exterior wall, a flow switch and a FDC.  No structure has 
a
GWW> check valve or an internal control valve.

GWW> I have been told that the ten to twelve structures are a single "building"
GWW> (the portions of which are simply separated by several scores of yards) and
GWW> therefore the control valve and check valve are in the one building that 
the
GWW> underground enters and exits after passing through the backflow preventer.
GWW> I am also being told that having no check valve between the FDC and the
GWW> hydrants is not a problem.

GWW> Both firsts for me.

GWW> I have looked through the standards and can not find chapter or verse on
GWW> which to base a response.  Any help would be greatly appreciated.

GWW> Thanks,
GWW> Garth


It is likely to be a building code thing (depending when and where it
was built), but the following has been in the IBC and BOCA (at least)
for along time:

"503.1.2 Buildings on same lot. Two or more buildings on the same lot
shall be regulated as separate buildings or shall be considered as
portions of one building if the height of each building and the
aggregate area of buildings are within the limitations of Table 503 as
modified by Sections 504 and 506. The provisions of this code
applicable to the aggregate building shall be applicable to each
building."

The operative word is "lot". If the buildings are not the same lot,
regardless of addresses and meet the other code criteria, it can be
considered one building.

-- 
Best regards,

 Dan Kaczor, Plans Examiner (but not a Guru to anyone)

[EMAIL PROTECTED]