Craig - The underground vales are not supervised, the location of some are
not even known.  Yes, the underground is ductile, not sure if the lead-ins
are ductile or copper as the individual risers are 2".  I agree the
underground set-up is typical.  Plans show each floor of each system, a
single set of calculation results has been provided for the entire project.
I do not know the type of alarm system but can not imagine it not notifying
a central station.  Neither do I know if an alarm from one of the individual
risers causes an alarm in all of the structures.

 I have just never run into a site where control valves are not present and
accessible or where there are no checks between the fdc and the hydrant.
All ten of these building parts will be out-of-service if there is a fire,
freeze-up or accidental discharge in any of the individual structures....at
least until the underground valve is located, a t-wrench found, and the
valve closed or the individual riser is disconnected and plugged.

Garth


----- Original Message ----- 
From: <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Wednesday, September 12, 2007 9:41 AM
Subject: RE: what makes a "building"


This doesn't sound like anything much different than a site with
multiple buildings served by a private fire main.  However there are a
few things that don't sound like they are what we would consider good
engineering practice and maybe even to the point of not being compliant
but again, without seeing it first hand or having more info that's hard
to tell.

It's not uncommon to come into an industrial park or campus and bring
the underground into a building or pit, enter the backflow then out to
the rest of the buildings on the site.  Is the underground piping
ductile with run-ins into the buildings?  I'd question the buried gate
valves in the roadway boxes, they are probably not monitored or secured,
but that wasn't stated specifically.  The shot-gun type riser assembly
with no check valve or control valve isn't that uncommon either, but
again not necessarily best practice but a cheap installation, probably
how the installer got the job in the first place.

The problems I can see is that the control valve in the yard (when able
to be found) could be closed and no one would know it.  So that's not
code compliant,  (no supervision), hopefully the flow switch is actually
connected to an NFPA 72 compliant fire alarm system which reports to
some sort of monitoring service?

The fact that there are FDC's on each "riser" yet no check valve makes
no sense.  On private loops often there is a single FDC tied into the
loop on the private side of the fire main at or near the Backflow
location and near a municipal hydrant.  When that's the case there are
often no FDC's at the individual buildings.  I've seen this
configuration accepted by various jurisdictions and Underwriters.

What a concoction of a sprinkler system.  Were there any riser placards,
proof of any hydraulic calcs?  Any inspection tags or reports?


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to