A question without a simple answer. From the building code a building is
merely defined as " Any structure used or intended for supporting or
sheltering any use or occupancy".  That in itself defines the difference
between a building and a structure.  A home is a building, a radio
transmission tower a structure.

With that said a covered mall is an example of a large multiuse single
building. Don't let the zoning issues steer you astray, theres no telling
what some land use law could allow. It is entirely possible that a building
could project over or require access through another lot, a deeded easement
is just one method to do this. The building code actually makes reference
that land use, i.e. zoning issues are outside the scope of the building
code.

If one desires to use the term building in the context of the building code
they must do so in complete compliance with the building code. Its simply
not acceptable to pick and choose the sections "that work".  With that said
in order for this complex of buildings to be considered a single building
the full width and breadth of the building code need be applied.  

First determine the occupancy (and more specifically the most stringent
occupancy) construction type, height and area. Add the building areas (also
referred to as the footprint) together.  This represents the total building
area just as we would do with a single large building. Now take all of this
information and review it utilzing Table 503 of the IBC. Can we build this
building in accordance with the table ?.  Either yes or no we must consider
the two modifiers that modify the tabular (the numbers found in the table)
height and area limitations. Fire Sprinklers and Open Frontage are two such
modifiers, verify if using either or both of these modifiers allows the
building to fall within the permissable (tabular + modifiers) building area.
This is essentially what 2006 IBC 503.1.2 (Buildings on same lot) says.

If the "building" in question has passed muster so far, then means of
egress(IBC Chapt 10) (number of exits, travel distance, etc) must be
considered.  Next consider the fire protection requirements (IBC Chapt 9)
(Sprinklers, Standpipes, Fire Alarms) .......  I think everyone gets the
idea and its not a simple process.  As a code official when this question
arises it is the design professional who must prove compliance not the other
way around.  A single large building will actually gravatate to a more
stringent construction type, means of egress and fire protection. (just to
name a few).

There is one example I'd like to share and that has to do with occupant
load. The IBC (2006 IBC 1004.2 for those who want to check) stipulates a
provision wherein the occupant load of a building may be increased beyond
that listed in the "Maximum Floor Area Allowances Per Occupant" Table
(1004.1.1). But to do this the designer is directed by the code section that
"all other requirements of the code are also met".  In other words theres a
synergy implied in the code. If you want a glass of milk (versus say a glass
of water) you need to buy the whole cow.  So no picking and choosing.

Hope that sheds some light on the whole thing. PS- Don't leave out the
requirements of NFPA-13,14, 20............

John Drucker
Fire Protection Subcode Official
Building Inspector
New Jersey

Safe Buildings Save Lives !