So you'd be flowing through the underground and whatever sprinkler system piping just to test a pump?
Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.lg.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer Sent: Wednesday, September 19, 2007 2:34 PM To: [email protected] Subject: RE: pump test header location Ron, Lets say you got a pump that requires 8" discharge pipe, your sprinkler bulk main is 6", and you decide to connect the test header to the end of the bulk main. Have you had any problems getting the test header calc to work? (never, rarely, sometimes, etc.) Ed Kramer Littleton, CO >It's more common to take the test header off the end of bulk main or >combine it with the FDC line if the header is remote from the pump room. > >Ron Fletcher >Aero Automatic >Phoenix, AZ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)