Adding to John's posting, sprinkler systems installed per 2006 IBC must be 
electrically supervised, with a few exceptions.  Supervision includes "critical 
air pressure" (Section 903.4).  Although this section does not say "per NFPA 
72", the next section requires distinctly different trouble, alarm and 
supervisory signals be sent to a central station, remote or proprietary 
supervising station, as defined by NFPA 72, or other approved, constantly 
attended location.  When I hear "electrically supervised" and that list of 
signals, I think NFPA 72.  Although a bit weak, the connection to 72 seems to 
be there.
   
  Also, take a look at 13-2002, Annex D.5.1, for a synopsis of the very similar 
set of NFPA 101 requirements for supervised sprinkler system.
   
  And as George says regarding cheap insurance, install the switch and let 
someone else figure out how and to where it gets wired.  Hopefully, someone 
will do that.
   
  Dave at Firetech Engineering Inc

John Drucker <[EMAIL PROTECTED]> wrote:
  
Here's the reference;

2002 NFPA-72 5.13.2.2(2) "A pressure supervisory signal initiating device
for a dry pipe sprinkler system shall indicated both high and low pressure
conditions. The off normal signal shall be initiated when the pressure
increases or decreases by 70kPa (10psi)."

2002 NFPA-72 is the 2006 IBC Chapter 35 Reference Standard.

John Drucker
Fire Protection Subcode Official
New Jersey

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to