I have not worked with FM much and I am hoping someone can verify my design is correct. 4,000 S.F. warehouse for carpet storage to max. 5'. Building is 14' sidewall, 17'-6" at the peak for 2/12 pitch. ELO-231 sprinklers spaced 100 S.F. max, .30/3000 per FM 8-30 table #1 no in-rack. One 1-1/2" hose station with 50 gpm inside and 450 outside hose. Minimum 7 psi end head pressure. Am I missing anything from FM??
Best regards, Joe Burtell, SET, CFPS byDesign LLC 3700 Banff Ave. Billings, MT 59102 Phone: 406.534.0167 Email: [EMAIL PROTECTED] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)