I have not worked with FM much and I am hoping someone can verify my design
is correct.
4,000 S.F. warehouse for carpet storage to max. 5'. Building is 14'
sidewall, 17'-6" at the peak for 2/12 pitch. ELO-231 sprinklers spaced 100
S.F. max, .30/3000 per FM 8-30 table #1 no in-rack. One 1-1/2" hose station
with 50 gpm inside and 450 outside hose. Minimum 7 psi end head pressure. Am
I missing anything from FM?? 

Best regards,