Looks like they dropped the 10 Psi requirement, last seen in 2-01 cut sheets.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- From: "Joe Burtell" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Tuesday, November 20, 2007 2:23 PM
Subject: Carpet Storage


I have not worked with FM much and I am hoping someone can verify my design
is correct.
4,000 S.F. warehouse for carpet storage to max. 5'. Building is 14'
sidewall, 17'-6" at the peak for 2/12 pitch. ELO-231 sprinklers spaced 100
S.F. max, .30/3000 per FM 8-30 table #1 no in-rack. One 1-1/2" hose station with 50 gpm inside and 450 outside hose. Minimum 7 psi end head pressure. Am
I missing anything from FM??