Joe,
It looks like your density, and remote area match the requirements of
table 1 from 8-30.
There area couple of things I might add to the plans, just to show the
owner/occupant that it's not just a matter of sprinklers and forget it:
1) maintain minimum 36" clearance below the sprinkler to the top of the
storage (2.3.3)
2) maintain 2" to 4" transverse flue space in racks, and 12"
longitudinal for back to back racks (2.3.1)
3) maintain at least 8'-0" clear space for every 100' length of the
racks (2.3.1)
4) if permanent heat and/or smoke vents are present they should be
manually operated only. (2.2.1)
5) sprinklers should be rated at 286 degrees (2.4.2)
6) water supply should be at least 2 hours in duration (2.4.5)
Also, if the K-factor is 11.2, the minimum pressure might be as high as
7.17 psi, based on 100 sq.ft. and .30 gpm/sqft density.
I'm also guessing that you're going to impress upon the owner that the
storage can't exceed 12'-0" above the floor without a review of the
sprinkler system design, and the possible addition of in-rack sprinklers.
See Mr. Hankins? I did pay attention to what you told me.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
Joe Burtell wrote:
I have not worked with FM much and I am hoping someone can verify my design
is correct.
4,000 S.F. warehouse for carpet storage to max. 5'. Building is 14'
sidewall, 17'-6" at the peak for 2/12 pitch. ELO-231 sprinklers spaced 100
S.F. max, .30/3000 per FM 8-30 table #1 no in-rack. One 1-1/2" hose station
with 50 gpm inside and 450 outside hose. Minimum 7 psi end head pressure. Am
I missing anything from FM??
Best regards,
Joe Burtell, SET, CFPS
byDesign LLC
3700 Banff Ave.
Billings, MT 59102
Phone: 406.534.0167
Email: [EMAIL PROTECTED]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)