Unfortunately you can make such a literal interpretation and ignore the intent is to put something on the male threads. That is except for areas where the mfg has imposed a best practice. Didn't BlazeMaster say NOT to use both on the sprinkler inserts??

Roland

On Dec 7, 2007, at 8:36 AM, Gary Stites wrote:

Here's one for you....

In Los Angeles on a high-rise building, we had a field inspector cite
NFPA 13, 6-5.1.3 (2002) as meaning we could use tape OR compound on pipe NOT both. Does anyone out there believe this is the intent of the code?
Or do you think the point of this passage is to NOT put these items on
the female threads?