I'm more interested in what everyone else is using.  The standard is very 
vague: "11.5.3.3 The exhaust pipe shall be covered with high temperature 
insulation or otherwise guarded to protect personnel from injury."

Ryan Peterson
Wayne Automatic Fire Sprinklers

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of å... ....
Sent: Friday, December 14, 2007 1:51 PM
To: [email protected]
Subject: Exhaust Insulation

why not use rock wool / mineral wool?  It is commonly used in UL listed 
Perimeter Fire Containment Systems.  One problem is vibrations and consequent 
shaking of material loose.  Frangible fibers below 10 microns get stuck in the 
alveolars and might / probably cause cancer (like asbestos, though that
is my guess only).   So I would wrap
it tight.  the other option is to do what the mechanical trades do with ducts 
running vertically between floors:  wrap it in a 1 hour chase (5/8 inch Type X 
rock) with minimum 18 inch clearance from combustible framing and have 
maintenance inspection ports.

would not semi- muffler shops have something more finely tuned to your 
challenge, though?

scot deal
excelsior fire


On 12/13/07, Ryan Peterson <[EMAIL PROTECTED]> wrote:
>
> Can anyone recommend a product for insulating diesel fire pump exhaust?
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to