The typical scenario I see with this is where we have a shell office or
retail space.  The shell space is typically designed for 1500+ sq ft.  Then,
when you drop in a ceiling, you often have the QR reduction that comes into
play for a reduced design area of 900 sq ft.  Now, with the arm overs and
such, I have not seen it throw off a calc when you are reducing the design
area by 600 sq ft.  I am not saying that it can't happen, but just that I
have never seen it.  However, if you did the shell with the QR reductions,
then you may be at a point where the extra arm overs and such do create a
problem for the calculated systems.

Also, if you are using some of the newer calc programs, it is pretty simple
to slap a remote area on the system and get it calc'd in a matter of a few
minutes.  You can then prove the point that it really is not an issue.

Travis 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe Hankins
Sent: Thursday, February 07, 2008 11:39 AM
To: [email protected]
Subject: Re: Arm over Calculations

Regardless off what one's interpretation of NFPA 13 is, the inescapable fact
is that adding arm overs (two elbows = 10+ feet of 1 in. pipe by
themselves) will throw the original calculations significantly off.

Joe

Craig Rauch wrote:
> My question is regarding an existing light hazard system. We are currently
using the 2002 NFPA 13.
>
> The system was calculated last year when this was a shell space as light
hazard. They are now fitting this space out, and have submitted plans
showing a number of arm overs and some additional heads to accommodate the
layout of the space.
>
> The question has now come up as to if we should require calculations.
>
> At what point would you say the calculations were needed for this type of
work?
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email 
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
>   

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

__________ NOD32 2856 (20080207) Information __________

This message was checked by NOD32 antivirus system.
http://www.eset.com


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to