Also, do not forget the tendency to catch 2 sprinklers from one outlet on
tenant upfits. I have been know to prove 2 sprinklers from one outlet on the
shell, and keep a copy in house, in anticipation of bidding/doing the
upfit...

R/

Matt

Matthew J. Willis
Living Water Fire Protection, LLC.
1160 McKenzie Rd.
PO Box 877
Cantonment, FL. 32533
850-937-1850 Voice
850-937-1852 Facsimile
[EMAIL PROTECTED]
 

----- >-----Original Message-----
----- >From: [EMAIL PROTECTED] 
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of George Church
----- >Sent: Thursday, February 07, 2008 1:47 PM
----- >To: [email protected]
----- >Subject: RE: Arm over Calculations
----- >
----- >IF you did the original......
----- >
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Travis Mack, SET
----- >Sent: Thursday, February 07, 2008 1:57 PM
----- >To: [email protected]
----- >Subject: RE: Arm over Calculations
----- >
----- >The typical scenario I see with this is where we have a 
----- >shell office or retail space.  The shell space is 
----- >typically designed for 1500+ sq ft.  Then, when you drop 
----- >in a ceiling, you often have the QR reduction that comes 
----- >into play for a reduced design area of 900 sq ft.  Now, 
----- >with the arm overs and such, I have not seen it throw 
----- >off a calc when you are reducing the design area by 600 
----- >sq ft.  I am not saying that it can't happen, but just 
----- >that I have never seen it.  However, if you did the 
----- >shell with the QR reductions, then you may be at a point 
----- >where the extra arm overs and such do create a problem 
----- >for the calculated systems.
----- >
----- >Also, if you are using some of the newer calc programs, 
----- >it is pretty simple to slap a remote area on the system 
----- >and get it calc'd in a matter of a few minutes.  You can 
----- >then prove the point that it really is not an issue.
----- >
----- >Travis 
----- >
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Joe Hankins
----- >Sent: Thursday, February 07, 2008 11:39 AM
----- >To: [email protected]
----- >Subject: Re: Arm over Calculations
----- >
----- >Regardless off what one's interpretation of NFPA 13 is, 
----- >the inescapable fact is that adding arm overs (two 
----- >elbows = 10+ feet of 1 in. pipe by
----- >themselves) will throw the original calculations 
----- >significantly off.
----- >
----- >Joe
----- >
----- >Craig Rauch wrote:
----- >> My question is regarding an existing light hazard 
----- >system. We are 
----- >> currently
----- >using the 2002 NFPA 13.
----- >>
----- >> The system was calculated last year when this was a 
----- >shell space as 
----- >> light
----- >hazard. They are now fitting this space out, and have 
----- >submitted plans showing a number of arm overs and some 
----- >additional heads to accommodate the layout of the space.
----- >>
----- >> The question has now come up as to if we should 
----- >require calculations.
----- >>
----- >> At what point would you say the calculations were 
----- >needed for this type 
----- >> of
----- >work?
----- >> _______________________________________________
----- >> Sprinklerforum mailing list
----- >> [email protected]
----- >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >>
----- >> To Unsubscribe, send an email
----- >> to:[EMAIL PROTECTED]
----- >> (Put the word unsubscribe in the subject field)
----- >>
----- >>   
----- >
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email 
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)
----- >
----- >__________ NOD32 2856 (20080207) Information __________
----- >
----- >This message was checked by NOD32 antivirus system.
----- >http://www.eset.com
----- >
----- >
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email 
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)
----- >
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email 
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to