Cliff, I'm not aware of anything in 13 that requires the check valve. Also worth noting, nothing in 13 requires that each floor has its own control valve (except for high rises, I think). I tried to find the section that requires the control valves in high rises but couldn't. Anyone know if it's been removed, or am I just missing it?
Ed Kramer Littleton, CO > -----Original Message----- > From: [EMAIL PROTECTED] [mailto:sprinklerforum- > [EMAIL PROTECTED] On Behalf Of Cliff Whitfield > Sent: Wednesday, February 13, 2008 1:50 PM > To: [email protected] > Subject: Check valve on floor control assembly > > NFPA 14 requires a check valve on a floor control assembly for a > connection > to a standpipe that is part of a combined system. (6.3.5.1 2007 ed) > Does > this requirement cross over to NFPA 13 for a riser in a multi-story > building > that is not actually a standpipe? Like for a 3-story bldg that isn't > high > enough to require a standpipe. > > > > I understand that it would be a good idea for the same reasons it is > required on a standpipe but is it actually a requirement? > > > > Cliff Whitfield, SET > > Fire Design, Inc. > > > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:Sprinklerforum- > [EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)