Cliff, I'm not aware of anything in 13 that requires the check valve.  Also
worth noting, nothing in 13 requires that each floor has its own control
valve (except for high rises, I think).  I tried to find the section that
requires the control valves in high rises but couldn't.  Anyone know if it's
been removed, or am I just missing it?

Ed Kramer
Littleton, CO

> -----Original Message-----
> From: [EMAIL PROTECTED] [mailto:sprinklerforum-
> [EMAIL PROTECTED] On Behalf Of Cliff Whitfield
> Sent: Wednesday, February 13, 2008 1:50 PM
> To: [email protected]
> Subject: Check valve on floor control assembly
> 
> NFPA 14 requires a check valve on a floor control assembly for a
> connection
> to a standpipe that is part of a combined system. (6.3.5.1 2007 ed)
> Does
> this requirement cross over to NFPA 13 for a riser in a multi-story
> building
> that is not actually a standpipe?  Like for a 3-story bldg that isn't
> high
> enough to require a standpipe.
> 
> 
> 
> I understand that it would be a good idea for the same reasons it is
> required on a standpipe but is it actually a requirement?
> 
> 
> 
> Cliff Whitfield, SET
> 
> Fire Design, Inc.
> 
> 
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email to:Sprinklerforum-
> [EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to