Ed,

I think you'll find in the all the building codes that two standpipes
are required in high rises. You'll then find in 14 the allowance for
using the standpipes as risers also as well as the requirement talked
about the last couple of days for check valves on looped systems.
Looped systems calc real well with two big risers so this becomes the
logical default design on high rises. Since you rarely see anything
else in a high rise the myth of it being a requirement comes into
existence. John can correct my code critical path on this but I
suspect that the original post came from this type of inductive logic.
I have a colleague that's dyslexic and probably the best code weenie I
know. The dyslexia causes him to have to trace every project he does
as if he knows no code. Although he does know it inside and out like
John he has to phyically critical path everything he does and
reference it so he can check his work. Since he does code analysis on
power generation facilities and other large scale projects that he can
support conclusions that effect projects in six and seven figure
increments is critical in itself.

On Thu, Feb 14, 2008 at 7:54 AM, Ed Kramer <[EMAIL PROTECTED]> wrote:
> Cliff, I'm not aware of anything in 13 that requires the check valve.  Also
>  worth noting, nothing in 13 requires that each floor has its own control
>  valve (except for high rises, I think).  I tried to find the section that
>  requires the control valves in high rises but couldn't.  Anyone know if it's
>  been removed, or am I just missing it?
>
>  Ed Kramer
>  Littleton, CO
>
>  > -----Original Message-----
>  > From: [EMAIL PROTECTED] [mailto:sprinklerforum-
>  > [EMAIL PROTECTED] On Behalf Of Cliff Whitfield
>  > Sent: Wednesday, February 13, 2008 1:50 PM
>  > To: [email protected]
>  > Subject: Check valve on floor control assembly
>  >
>  > NFPA 14 requires a check valve on a floor control assembly for a
>  > connection
>  > to a standpipe that is part of a combined system. (6.3.5.1 2007 ed)
>  > Does
>  > this requirement cross over to NFPA 13 for a riser in a multi-story
>  > building
>  > that is not actually a standpipe?  Like for a 3-story bldg that isn't
>  > high
>  > enough to require a standpipe.
>  >
>  >
>  >
>  > I understand that it would be a good idea for the same reasons it is
>  > required on a standpipe but is it actually a requirement?
>  >
>  >
>  >
>  > Cliff Whitfield, SET
>  >
>  > Fire Design, Inc.
>  >
>  >
>  >
>  >
>  >
>  > _______________________________________________
>  > Sprinklerforum mailing list
>  > [email protected]
>  > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>  >
>  > To Unsubscribe, send an email to:Sprinklerforum-
>  > [EMAIL PROTECTED]
>  > (Put the word unsubscribe in the subject field)
>
>  _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  To Unsubscribe, send an email to:[EMAIL PROTECTED]
>  (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to