Do "THEY" have an amendment for that restriction (since there are
more than a few CA amendments). That would be no different than the
conversation I had yesterday about the AHJ requiring a sprinkler in
the ceiling pocket because he didn't like not having one in it.
Speaking of CA amendments, there are certainly some interesting one
being entertained as part of adopting the 07 edition. For axmple,
"THEY" want to delete 8.6.5.2.1.4 whereby obstructions greater than
18 inches below the sprinkler in Light and Ordinary hazard only
structural members need to be considered (ignore the others - that is
once you get past the beam rule). The TC had a basis for this
allowance. I wonder what the basis is for deleting it? I'm flashing
back to Blazing Saddles.
Roland
On Feb 14, 2008, at 8:32 AM, Gary Stites wrote:
I've never been allowed to calc the "cross connected" system on a high
rise as a loop. They've only allowed us to calc a single source
with the
other source being redundant.
Gary Stites
Vice President: Southern California
RLH Fire Protection
3430 Unicorn Road
Bakersfield, Ca. 93308
661-322-9344 #1343
Direct Line 661-410-1343
Direct FAX 866-871-2237
[EMAIL PROTECTED]
www.rlhfp.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)