In NFPA 13, 2007 look at Figures A.8.17.4.2(b) for the typical multi-story building floor control valve assembly, No check valve.
Figures A.18.17.5.2.2(a) and (b) show the check valve in the assembly due to it being a combined sprinkler riser/standpipe. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.lg.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman Sent: Thursday, February 14, 2008 11:09 AM To: [email protected] Subject: Re: Check valve on floor control assembly Ed, I think you'll find in the all the building codes that two standpipes are required in high rises. You'll then find in 14 the allowance for using the standpipes as risers also as well as the requirement talked about the last couple of days for check valves on looped systems. Looped systems calc real well with two big risers so this becomes the logical default design on high rises. Since you rarely see anything else in a high rise the myth of it being a requirement comes into existence. John can correct my code critical path on this but I suspect that the original post came from this type of inductive logic. I have a colleague that's dyslexic and probably the best code weenie I know. The dyslexia causes him to have to trace every project he does as if he knows no code. Although he does know it inside and out like John he has to phyically critical path everything he does and reference it so he can check his work. Since he does code analysis on power generation facilities and other large scale projects that he can support conclusions that effect projects in six and seven figure increments is critical in itself. On Thu, Feb 14, 2008 at 7:54 AM, Ed Kramer <[EMAIL PROTECTED]> wrote: > Cliff, I'm not aware of anything in 13 that requires the check valve. > Also worth noting, nothing in 13 requires that each floor has its own > control valve (except for high rises, I think). I tried to find the > section that requires the control valves in high rises but couldn't. > Anyone know if it's been removed, or am I just missing it? > > Ed Kramer > Littleton, CO > > > -----Original Message----- > > From: [EMAIL PROTECTED] > [mailto:sprinklerforum- > [EMAIL PROTECTED] On Behalf Of > Cliff Whitfield > Sent: Wednesday, February 13, 2008 1:50 PM > To: > [email protected] > Subject: Check valve on floor > control assembly > > NFPA 14 requires a check valve on a floor > control assembly for a > connection > to a standpipe that is part of > a combined system. (6.3.5.1 2007 ed) > Does > this requirement cross > over to NFPA 13 for a riser in a multi-story > building > that is > not actually a standpipe? Like for a 3-story bldg that isn't > high > > enough to require a standpipe. > > > > > > > > I understand that it would be a good idea for the same reasons it > is > required on a standpipe but is it actually a requirement? > > > > > > > > Cliff Whitfield, SET > > > > Fire Design, Inc. > > > > > > > > > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > To Unsubscribe, send an email to:Sprinklerforum- > > [EMAIL PROTECTED] > (Put the word unsubscribe in the subject > field) > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email > to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)
