In NFPA 13, 2007 look at Figures A.8.17.4.2(b) for the typical
multi-story building floor control valve assembly, No check valve.

Figures A.18.17.5.2.2(a) and (b) show the check valve in the assembly
due to it being a combined sprinkler riser/standpipe.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron
Greenman
Sent: Thursday, February 14, 2008 11:09 AM
To: [email protected]
Subject: Re: Check valve on floor control assembly

Ed,

I think you'll find in the all the building codes that two standpipes
are required in high rises. You'll then find in 14 the allowance for
using the standpipes as risers also as well as the requirement talked
about the last couple of days for check valves on looped systems.
Looped systems calc real well with two big risers so this becomes the
logical default design on high rises. Since you rarely see anything else
in a high rise the myth of it being a requirement comes into existence.
John can correct my code critical path on this but I suspect that the
original post came from this type of inductive logic.
I have a colleague that's dyslexic and probably the best code weenie I
know. The dyslexia causes him to have to trace every project he does as
if he knows no code. Although he does know it inside and out like John
he has to phyically critical path everything he does and reference it so
he can check his work. Since he does code analysis on power generation
facilities and other large scale projects that he can support
conclusions that effect projects in six and seven figure increments is
critical in itself.

On Thu, Feb 14, 2008 at 7:54 AM, Ed Kramer <[EMAIL PROTECTED]> wrote:
> Cliff, I'm not aware of anything in 13 that requires the check valve.

> Also  worth noting, nothing in 13 requires that each floor has its own

> control  valve (except for high rises, I think).  I tried to find the 
> section that  requires the control valves in high rises but couldn't.

> Anyone know if it's  been removed, or am I just missing it?
>
>  Ed Kramer
>  Littleton, CO
>
>  > -----Original Message-----
>  > From: [EMAIL PROTECTED] 
> [mailto:sprinklerforum-  > [EMAIL PROTECTED] On Behalf Of 
> Cliff Whitfield  > Sent: Wednesday, February 13, 2008 1:50 PM  > To: 
> [email protected]  > Subject: Check valve on floor 
> control assembly  >  > NFPA 14 requires a check valve on a floor 
> control assembly for a  > connection  > to a standpipe that is part of

> a combined system. (6.3.5.1 2007 ed)  > Does  > this requirement cross

> over to NFPA 13 for a riser in a multi-story  > building  > that is 
> not actually a standpipe?  Like for a 3-story bldg that isn't  > high

> > enough to require a standpipe.
>  >
>  >
>  >
>  > I understand that it would be a good idea for the same reasons it 
> is  > required on a standpipe but is it actually a requirement?
>  >
>  >
>  >
>  > Cliff Whitfield, SET
>  >
>  > Fire Design, Inc.
>  >
>  >
>  >
>  >
>  >
>  > _______________________________________________
>  > Sprinklerforum mailing list
>  > [email protected]
>  > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>  >
>  > To Unsubscribe, send an email to:Sprinklerforum-  > 
> [EMAIL PROTECTED]  > (Put the word unsubscribe in the subject 
> field)
>
>  _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  To Unsubscribe, send an email 
> to:[EMAIL PROTECTED]
>  (Put the word unsubscribe in the subject field)
>



--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to