It say equipped throughout in accordance with NFPA 13. Omitting sprinklers in a non-combustible concealed space is in accordance with NFPA 13, so the building is equipped thoroughout.
Would he expect to see sprinklers under desks, inside wall cavities, inside ductwork, etc.? Paul J. Pinigis, P.E. Chief Life Safety Engineer -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Randy Knutson Sent: Thursday, February 14, 2008 2:19 PM To: [email protected] Subject: Fully Sprinklered Definition Forum Members, When it says in the IFC (section 903.1.1 2003ed) to "Equip Throughout" with sprinkler system, does omitting sprinklers above ceilings in non-combustible construction (per NFPA 13:8.14.1.2.2 2002ed) make it not "equipped throughout"? I have an I-3 occupancy in a Type 1 B building. The inspector says I need sprinklers above the ceiling. Are they really required there? Thanks for any help. Randy Knutson Shilo Automatic Sprinkler, Inc. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)