It say equipped throughout in accordance with NFPA 13.  Omitting
sprinklers in a non-combustible concealed space is in accordance with
NFPA 13, so the building is equipped thoroughout.  

Would he expect to see sprinklers under desks, inside wall cavities,
inside ductwork, etc.?

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Randy
Knutson
Sent: Thursday, February 14, 2008 2:19 PM
To: [email protected]
Subject: Fully Sprinklered Definition

Forum Members,

 

When it says in the IFC (section 903.1.1 2003ed) to "Equip Throughout"
with
sprinkler system, does omitting sprinklers above ceilings in
non-combustible
construction (per NFPA  13:8.14.1.2.2 2002ed) make it not "equipped
throughout"?

I have an I-3 occupancy in a Type 1 B building. The inspector says I
need
sprinklers above the ceiling. Are they really required there?

 

Thanks for any help.

 

Randy Knutson

Shilo Automatic Sprinkler, Inc.