I agree with Art. A horizontal split case pump takes suction from both sides of the impeller, so non-laminar flow can mess with it. Thus the requirements of the sections you mention. An inline pump takes suction from only one side of the impeller. Non-laminar flow isn't a critical issue and those sections only reference horizontal split case pumps.
Ed Kramer Littleton, CO > -----Original Message----- > From: [EMAIL PROTECTED] [mailto:sprinklerforum- > [EMAIL PROTECTED] On Behalf Of Jamie Seidl > Sent: Friday, February 15, 2008 9:22 AM > To: [email protected] > Subject: Vertical Inline > > Forum, > We are having a discussion in our office about pumps. I have always > thought that a vertical in-line pump didn't need to have the 10 pipe > diameter distance on the suction side since 5.14.6.3.1, 5.14.6.3.2, and > 5.14.6.3.3 all reference "horizontal split case pumps. > > Have I missed something? > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:Sprinklerforum- > [EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)