This is a repeat, as my previous e-mail somehow never got posted.

A building is being used for manufacuring Glass fiber reinforced resin
products. (I think the products are bath tubs etc., but not sure yet). Some
material used, such as Polyester Resins, Methyl Ethyl Ketone Peroxyde
(MEKP), Acetone etc. are class 1C flammable liquids. 

The owner states that "Polyester resins will be stored in resin rooms.
Acetone in certified containers throughout shop space. And MEKP catalysts
will be stored in certified containers at workstations. Also, composite
plastic molds will be stored on racks, 5 to 12 feet high."

The engineer of record has specified OH2 for the building and when
questioned is directing to NFPA 33, 2000, section 15.3. 

I think the storage areas have to be designed as per NFPA 30 for flammable
liquids, and as per NFPA 13 for plastic storage. Will the storage quantities
be a deciding factor (for selecting OH2)?

Will the process areas and spray application areas be OH2 (as per NFPA 33)?

Tony 