Roland is correct and that is how most jurisdictions interpret NFPA 13. As a matter of fact, the IFC, IBC and IRC (as an appendix item) all refer to NFPA 13, 13R and 13D.
I would ask to have the Building Official/AHJ make a ruling rather than trust an inspector's opinion. Type 1B construction is considered wholly non-combustible in the first place. Mark J. Finocchio Fire Captain Lenexa, KS Fire Department [EMAIL PROTECTED] Direct: 913.477.7920 Fax: 913.888.2143 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Roland Huggins Sent: Thursday, February 14, 2008 1:44 PM To: [email protected] Subject: [SPAM] - Re: Fully Sprinklered Definition - Email has different SMTP TO: and MIME TO: fields in the email addresses the building code says: ..sprinkler systems shall be installed throughout in accordance with NFPA 13. That means the areas that are allowed omission of sprinklers still provides protection throughout. It says the same thing on 13R (for which many trade-ups are allowed) and the building is considered sprinklered throughout with the attic and concealed combustible spaces having no protection. Roland On Feb 14, 2008, at 11:19 AM, Randy Knutson wrote: > Forum Members, > > > > When it says in the IFC (section 903.1.1 2003ed) to "Equip > Throughout" with > sprinkler system, does omitting sprinklers above ceilings in non- > combustible > construction (per NFPA 13:8.14.1.2.2 2002ed) make it not "equipped > throughout"? > > I have an I-3 occupancy in a Type 1 B building. The inspector says > I need > sprinklers above the ceiling. Are they really required there? > > > > Thanks for any help. > > > > Randy Knutson > > Shilo Automatic Sprinkler, Inc. > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:Sprinklerforum- > [EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) CONFIDENTIALITY NOTICE: This e-mail, including any files transmitted with it, is the property of the City of Lenexa, Kansas. It is confidential and is intended solely for the use of the individual, or entity, to whom the e-mail is addressed. If you are not the named recipient, or otherwise have reason to believe that you have received this message in error, please notify the sender at (913) 477-7500 and delete this message immediately from your computer. Any other use, retention, dissemination, forwarding, printing, or copying of this e-mail is strictly prohibited. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)