Roland is correct and that is how most jurisdictions interpret NFPA 13.
As a matter of fact, the IFC, IBC and IRC (as an appendix item) all
refer to NFPA 13, 13R and 13D.

I would ask to have the Building Official/AHJ make a ruling rather than
trust an inspector's opinion.  Type 1B construction is considered wholly
non-combustible in the first place.  

Mark J. Finocchio
Fire Captain
Lenexa, KS Fire Department
 
[EMAIL PROTECTED]
 
Direct: 913.477.7920
Fax:    913.888.2143
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Thursday, February 14, 2008 1:44 PM
To: [email protected]
Subject: [SPAM] - Re: Fully Sprinklered Definition - Email has different
SMTP TO: and MIME TO: fields in the email addresses

the building code says: ..sprinkler systems shall be installed  
throughout in accordance with NFPA 13.
That means the areas that are allowed omission of sprinklers still  
provides protection throughout.

It says the same thing on 13R (for which many trade-ups are allowed)  
and the building is considered sprinklered throughout with the attic  
and concealed combustible spaces having no protection.


Roland

On Feb 14, 2008, at 11:19 AM, Randy Knutson wrote:

> Forum Members,
>
>
>
> When it says in the IFC (section 903.1.1 2003ed) to "Equip  
> Throughout" with
> sprinkler system, does omitting sprinklers above ceilings in non- 
> combustible
> construction (per NFPA  13:8.14.1.2.2 2002ed) make it not "equipped
> throughout"?
>
> I have an I-3 occupancy in a Type 1 B building. The inspector says  
> I need
> sprinklers above the ceiling. Are they really required there?
>
>
>
> Thanks for any help.
>
>
>
> Randy Knutson
>
> Shilo Automatic Sprinkler, Inc.
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:Sprinklerforum- 
> [EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

CONFIDENTIALITY NOTICE:

This e-mail, including any files transmitted with it, is the property of the 
City of Lenexa, Kansas.  It is confidential and is intended solely for the use 
of the individual, or entity, to whom the e-mail is addressed.  If you are not 
the named recipient, or otherwise have reason to believe that you have received 
this message in error, please notify the sender at (913) 477-7500 and delete 
this message immediately from your computer.  Any other use, retention, 
dissemination, forwarding, printing, or copying of this e-mail is strictly 
prohibited.


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to