Tyco makes a dry pendent head and sells a boot to seal out any
infiltrating air which is usually where the condensation comes from.
Also be sure the head is the recommended length. 

B K

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of GAYLE
KNOWLES
Sent: Tuesday, February 19, 2008 3:30 PM
To: sprinklerforum
Subject: dry pendant in cooler


We have a situation with a dry pendant located minimum 24" away from
coil in a cooler.  Apparantly, condensation is building up on head and
dripping water on cooler floor.  This is a cooler box at a Walgreens.
Box is very narrow and really no other place to put head.  Has anyone
experienced this before and come up with an idea to correct this
problem?  Walgreen's is telling us to put a baffle between head and
coil.  Not a good idea, altho, box is small enough that head will flood
entire area, but baffle adds an obstruction.  Thanks for any ideas or
help.  I actually told them, coil was running too cool.  Go figure...I
am not a refrigeration person.  