actually, this is a "cooler".  But, I'm going with all of your advise and going 
to make sure everything is sealed and double sealed.

Gayle Knowles, SET 

> From: [EMAIL PROTECTED]
> To: [email protected]
> Date: Tue, 19 Feb 2008 16:17:14 -0700
> Subject: Re: dry pendant in cooler
> 
> Tyco says 12" for -20'F, 18" for -40'F and 24" for -60'F, the only part that 
> is unclear is if that is total length or the length above the 
> cooler/freezer. We typically just order all 24". We rarely see -60 freezers.
> 
> Thom McMahon
> Firetech, Inc.
> 2560 Copper Ridge Dr
> Steamboat Springs, CO 80488-2136
> Tel: 970-879-7952
> Fax: 970-879-7926
> ----- Original Message ----- 
> From: <[EMAIL PROTECTED]>
> To: <[email protected]>
> Sent: Tuesday, February 19, 2008 3:35 PM
> Subject: RE: dry pendant in cooler
> 
> 
> What is the length of the dry pendant?  Isn't typical mfgr.
> recommendation like 12" minimum?
> 
> 
> Craig L. Prahl, CET
> Fire Protection Group
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [EMAIL PROTECTED]
> http://www.lg.com
> 
> 
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Thom
> McMahon
> Sent: Tuesday, February 19, 2008 4:53 PM
> To: [email protected]
> Subject: Re: dry pendant in cooler
> 
> We've found that even when using the DSB-1 (Rubber Boot) for our dry
> sprinkler heads we need to foam around the heads in freezers and coolers
> to prevent condensation. The first time someone walks on the
> cooler/freezer roof/ceiling it can break the seal and allow condensation
> on the head.
> 
> Thom McMahon
> Firetech, Inc.
> 2560 Copper Ridge Dr
> Steamboat Springs, CO 80488-2136
> Tel: 970-879-7952
> Fax: 970-879-7926
> ----- Original Message -----
> From: "Chris Payne" <[EMAIL PROTECTED]>
> To: <[email protected]>
> Sent: Tuesday, February 19, 2008 1:34 PM
> Subject: Re: dry pendant in cooler
> 
> 
> >I have had this happen before and it was due to sealing the head
> >penetration. We drilled a 2" min. hole and sealed around the head with
> >spray foam. That solved the problem.
> >
> > Chris Payne
> > FPS
> >
> > ----- Original Message ----- 
> > From: "GAYLE KNOWLES" <[EMAIL PROTECTED]>
> > To: "sprinklerforum" <[email protected]>
> > Sent: Tuesday, February 19, 2008 2:29 PM
> > Subject: dry pendant in cooler
> >
> >
> >
> > We have a situation with a dry pendant located minimum 24" away from
> coil
> > in a cooler.  Apparantly, condensation is building up on head and
> dripping
> > water on cooler floor.  This is a cooler box at a Walgreens. Box is
> very
> > narrow and really no other place to put head.  Has anyone experienced
> this
> > before and come up with an idea to correct this problem?  Walgreen's
> is
> > telling us to put a baffle between head and coil.  Not a good idea,
> altho,
> > box is small enough that head will flood entire area, but baffle adds
> an
> > obstruction.  Thanks for any ideas or help.  I actually told them,
> coil
> > was running too cool.  Go figure...I am not a refrigeration person.
> >
> > Gayle Knowles, SET
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> >
> >
> > -- 
> > No virus found in this incoming message.
> > Checked by AVG Free Edition.
> > Version: 7.5.516 / Virus Database: 269.20.8/1287 - Release Date:
> 2/19/2008
> > 10:55 AM
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> >
> >
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to