sounds like a perfect storage spot for a dry head to me.......

----- Original Message ----- 
From: "GAYLE KNOWLES" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Wednesday, February 20, 2008 9:07 AM
Subject: RE: dry pendant in cooler



Yes, and now they've decided that they want a pvc tube with a screwed cap
mounted on the wall in the riser room with the extra dry pendant in there



> Date: Tue, 19 Feb 2008 21:04:43 -0500
> From: [EMAIL PROTECTED]
> To: [email protected]
> Subject: RE: dry pendant in cooler
>
> If you have the same Walgreen specs we have you will need to order an
extra 24" dry drop to fasten to the pipe above the cooler.
>
> Bobby McCullough
> Allsouth Sprinkler
>
> ________________________________
>
> From: [EMAIL PROTECTED] on behalf of GAYLE KNOWLES
> Sent: Tue 2/19/2008 6:36 PM
> To: [email protected]
> Subject: RE: dry pendant in cooler
>
>
>
>
> 24" minimum is the spec.  Of course, they are "exactly" 24"...especially
when you pay by the inch.
>
> Gayle Knowles, SET
> Regional Manager
> Kaufman Fire Protection Systems. Inc.
> 1319 Marmy Rd.
> Tempe, AZ.  85281
> PH:480-557-0475
>
> > Date: Tue, 19 Feb 2008 15:35:23 -0700
> > From: [EMAIL PROTECTED]
> > To: [email protected]
> > Subject: RE: dry pendant in cooler
> >
> > What is the length of the dry pendant?  Isn't typical mfgr.
> > recommendation like 12" minimum?
> >
> >
> > Craig L. Prahl, CET
> > Fire Protection Group
> > Mechanical Department
> > CH2MHILL
> > Lockwood Greene
> > 1500 International Drive
> > PO Box 491, Spartanburg, SC  29304-0491
> > Direct - 864.599.4102
> > Fax - 864.599.8439
> > [EMAIL PROTECTED]
> > http://www.lg.com
> >
> >
> > -----Original Message-----
> > From: [EMAIL PROTECTED]
> > [mailto:[EMAIL PROTECTED] On Behalf Of Thom
> > McMahon
> > Sent: Tuesday, February 19, 2008 4:53 PM
> > To: [email protected]
> > Subject: Re: dry pendant in cooler
> >
> > We've found that even when using the DSB-1 (Rubber Boot) for our dry
> > sprinkler heads we need to foam around the heads in freezers and coolers
> > to prevent condensation. The first time someone walks on the
> > cooler/freezer roof/ceiling it can break the seal and allow condensation
> > on the head.
> >
> > Thom McMahon
> > Firetech, Inc.
> > 2560 Copper Ridge Dr
> > Steamboat Springs, CO 80488-2136
> > Tel: 970-879-7952
> > Fax: 970-879-7926
> > ----- Original Message -----
> > From: "Chris Payne" <[EMAIL PROTECTED]>
> > To: <[email protected]>
> > Sent: Tuesday, February 19, 2008 1:34 PM
> > Subject: Re: dry pendant in cooler
> >
> >
> > >I have had this happen before and it was due to sealing the head
> > >penetration. We drilled a 2" min. hole and sealed around the head with
> > >spray foam. That solved the problem.
> > >
> > > Chris Payne
> > > FPS
> > >
> > > ----- Original Message -----
> > > From: "GAYLE KNOWLES" <[EMAIL PROTECTED]>
> > > To: "sprinklerforum" <[email protected]>
> > > Sent: Tuesday, February 19, 2008 2:29 PM
> > > Subject: dry pendant in cooler
> > >
> > >
> > >
> > > We have a situation with a dry pendant located minimum 24" away from
> > coil
> > > in a cooler.  Apparantly, condensation is building up on head and
> > dripping
> > > water on cooler floor.  This is a cooler box at a Walgreens. Box is
> > very
> > > narrow and really no other place to put head.  Has anyone experienced
> > this
> > > before and come up with an idea to correct this problem?  Walgreen's
> > is
> > > telling us to put a baffle between head and coil.  Not a good idea,
> > altho,
> > > box is small enough that head will flood entire area, but baffle adds
> > an
> > > obstruction.  Thanks for any ideas or help.  I actually told them,
> > coil
> > > was running too cool.  Go figure...I am not a refrigeration person.
> > >
> > > Gayle Knowles, SET
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]
> > > (Put the word unsubscribe in the subject field)
> > >
> > >
> > > --
> > > No virus found in this incoming message.
> > > Checked by AVG Free Edition.
> > > Version: 7.5.516 / Virus Database: 269.20.8/1287 - Release Date:
> > 2/19/2008
> > > 10:55 AM
> > >
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]
> > > (Put the word unsubscribe in the subject field)
> > >
> > >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email
to:[EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to