we had a similar scenario and approached AHJ with it.  He said to treat room as 
OH group 2 and add 5 closet heads to calcs.  He sent us a letter advising us to 
that affect.  



> From: [EMAIL PROTECTED]
> To: [email protected]
> Date: Sat, 23 Feb 2008 09:40:06 +1100
> Subject: Re: Gaggle of closets
> 
> Could you foresee a fire senario where the 47 extra heads would operate.  I 
> think that this is exactly what the exception is for.
> 
> Regards
> 
> 
> ----- Original Message -----
> From: "Paul Pinigis" [EMAIL PROTECTED]
> Sent: 22/02/2008 05:30 PM EST
> To: <[email protected]>
> Subject: RE: Gaggle of closets
> 
> 
> 
> Don't you just love it when the letter of the code works in your favor.
> I really don't think that this is what the NFPA 13 committee had in mind
> when they developed that section.
> 
> Paul J. Pinigis, P.E.
> Chief Life Safety Engineer
> 
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Todd
> Williams - FPDC
> Sent: Friday, February 22, 2008 5:05 PM
> To: [email protected]
> Subject: Gaggle of closets
> 
> I am looking an apartment building which is to be designed according
> to NFPA 13. On the first level, there is a room which contains 55 -
> 3'x5' tenant storage closets (mostly filled with shelves). These
> would need to be sprinklered, which is fine, but the issue comes in
> the hydraulics. Section 14.4.4.4.2 states that closets with a single
> sprinkler may be omitted from the calculation. There could be up to
> 47 closets in the remote area. I have used this exception numerous
> times, but never in this quantity. The standard says nothing to the
> contrary, so I could eliminate 47 sprinklers in the remote area
> because they are in closets? Is there something I am overlooking?
> 
> 
> 
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
> 
> 
> This document should only be read by those persons to whom it is addressed 
> and is not intended to be relied upon by any person without subsequent 
> written confirmation of its contents. Accordingly, our company disclaim all 
> responsibility and accept no liability (including in negligence) for the 
> consequences for any person acting, or refraining from acting, on such 
> information prior to the receipt by those persons of subsequent written 
> confirmation.
> 
> If you have received this e-mail message in error, please notify us 
> immediately by telephone. Please also destroy and delete the message from 
> your computer. The Unsolicited Electronic Message Act 2007 (The Spam Act) 
> came into effect from 5 September 2007. As a valued client you may receive 
> communications from us from time to time, including electronic publications, 
> invitations and related information. Please advise if you wish us to stop 
> sending these communications to you. Otherwise we will assume you wish to 
> continue receiving these communications from us. 
> 
> Any form of reproduction, dissemination, copying, disclosure, modification, 
> distribution and/or publication of this e-mail message is strictly prohibited.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to