whether or not 13D is used in a townhouse is currently allowed by the building code depending on HOW you define townhouse. Starting with the IRC, townhouse is 3 or more dwelling units within a building (all on one plot of land) with each dwelling unit going from slab to the roof. This only requires fire partitions between the units. It can NOT apply a 13D system but can use 13R. A townhouse that is an individual unit on one plot of lane and the adjacent unit butts up to it with zero clearance, ie a common wall required to be a fire wall (will remain standing if the building on either side collapses) can apply a 13D system. It makes more sense to refer to the latter as a rowhouse.

The NFPA 13D committee addressed a proposal on just this issue. The official ballot is not yet out plus it is just the ROP stage and I certainly expect "some" refinement at the ROC stage.

The first defined type is built under the IRC and the second under the IBC.

Roland

On Feb 26, 2008, at 11:15 AM, Greg McGahan wrote:

We are beginning to see more 13d installations here and I know some of you disagree but one of the local AHJ's only require 13d systems in townhomes.