This issue has caused a lot of inappropriate zoning layouts. The alarm section of the IBC (907) is stating that you have to include the water switch as a zone BUT it does not dictate the number and size of the sprinkler zones. That is driven by the sprinkler section of the IBC (903).

There are other code sections that support this so don't read just this one section and place too much emphasis on the AND pushing all the other requirement of 907 onto the sprinkler system.

Roland

On Mar 11, 2008, at 7:02 AM, Charles Thurston wrote:

In my opinion I would have to agree all AID's should be zoned by floor. This is due to the use of the word "AND" in the following line. If the word
was "OR" I would be on your side of the fence.

"Alarm initiating devices" are given as "heat detectors,
waterflow switches and manual stations".
                     ^^^