We discussed that section and it states "around or away from objects during
installation".  This is not the case; the deflection is cause by the
ductwork pushing down on the plastic pipe.  The permissible bending
deflection does not state that the deflection can be cause by something
pushing on the pipe.  Am I miss interpreting "around and away" to mean it
cannot forced by contact?

Thanks,
Gregg Fontes
Cen-Cal Fire Systems, Inc.
(209)334-9119

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: Thursday, March 13, 2008 10:23 AM
To: [email protected]
Subject: Re: Plastic Pipe bowing

Blazemaster (TYCO) installation instructions & tech handbook Jan 2005 lists 
Permissible bending deflections in table "J" based upon size of pipe and 
length.
Example: 1" cpvc is allowed to bend or deflect 6.3" in 5'-0" (5'-0" also 
just happens to be the max hanger spacing for 1".
Sounds like you have a compound deflection (bow) so 1/2 the allowed would 
seem appropriate.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- 
From: "Gregg Fontes" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Thursday, March 13, 2008 11:04 AM
Subject: Plastic Pipe bowing


>I was asked by a fire inspector if it is allowed to have mechanical 
>ductwork
> bow plastic pipe?  The ductwork is not support by the plastic pipe.  It is
> in a tight spot where the ductwork is installed above the plastic pipe and
> due to the limited space, it is bowing the pipe.  What the picture shows 
> is
> it looks like there is about 16" of space between the pipe and deck and 
> the
> 18" diameter flex is above the pipe.  This is bowing the plastic pipe. 
> The
> inspector is saying that they can't find anything in code that would not
> allow this.  They don't like it, but can't find anything to hang the hat 
> on.
>
>
> Thanks,
> Gregg Fontes
> Cen-Cal Fire Systems, Inc.
> (209)334-9119
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]