Hello RFI, In my opinion. I don't see it as much different than a "Floor Control Valve", Just horizontal floors.
YES I would put in a valve with supervision switches and Advise the owner it needs to be connected by his alarm company as a supervisory point. Monday, March 17, 2008, 6:05:13 PM, you wrote: > > Have a fairly small facility (<60 Heads); typical “U” shaped building; the > owner is requesting that prior to going into each “wing” a ball valve be > placed to be able to shut down that side of the wing for maintenance > purposes... the AHJ – who also wears the hat as the buildings’ maintenance > super’ –was contacted by the owner to request this scenario – to which he > (AHJ) has approved. > > Couple questions I have after reading 13R 2007; 5.2.12.4.4 and 6.7.1.2: > > (1) Acceptable installation then? (I’m leaning towards “yes”) > (2) Supervised? > (3) Non-supervised? > > Only reason for #2 & #3 is because they (NFPA sections) don’t ‘compliment’ > one another – yet they don’t “contradict” either. 5.2.12.4.4 states that > you can use one… doesn’t state that it needs to be supervised where 6.7.1.2 > states otherwise… > > Any help or insight would be appreciated!! > > RFI Chuck > > > > > > > No virus found in this outgoing message. > Checked by AVG. > Version: 7.5.519 / Virus Database: 269.21.7/1332 - Release Date: 3/17/2008 > 10:48 AM > > -- Best regards, Charles Thurston CET Coastal Fire Protection Coastal mailto:[EMAIL PROTECTED] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)