In my opinion. I don't see it as much different than a "Floor Control Valve", 
Just horizontal floors.

YES I would put in a valve with supervision switches and Advise the owner it 
needs to be connected by his alarm company as a supervisory point.

Monday, March 17, 2008, 6:05:13 PM, you wrote:

>  

> Have a fairly small facility (<60 Heads); typical “U” shaped building; the
> owner is requesting that prior to going into each “wing” a ball valve be
> placed to be able to shut down that side of the wing for maintenance
> purposes...  the AHJ – who also wears the hat as the buildings’ maintenance
> super’ –was contacted by the owner to request this scenario – to which he
> (AHJ) has approved. 

>  

> Couple questions I have after reading 13R 2007; 5.2.12.4.4 and 6.7.1.2:

>  

> (1)       Acceptable installation then?  (I’m leaning towards “yes”)

> (2)      Supervised?

> (3)      Non-supervised?

>  

> Only reason for #2 & #3 is because they (NFPA sections) don’t ‘compliment’
> one another – yet they don’t “contradict” either.  5.2.12.4.4 states that
> you can use one… doesn’t state that it needs to be supervised where 6.7.1.2
> states otherwise…

>  

> Any help or insight would be appreciated!!

>  

> RFI Chuck

>  

>  

>  

>  

>  

>  


> No virus found in this outgoing message.
> Checked by AVG. 
> Version: 7.5.519 / Virus Database: 269.21.7/1332 - Release Date: 3/17/2008
> 10:48 AM
>  
>   



-- 
Best regards,
Charles Thurston CET
Coastal Fire Protection
 Coastal                            mailto:[EMAIL PROTECTED]


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to