IBC states all control valves shall be supervised

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Matthew J.
Willis
Sent: Tuesday, March 18, 2008 12:15 PM
To: [email protected]
Subject: RE: a non-typical type installation question...

Isn't there also a requirement in 101 for valve supervision (Chap 9).,,?
That may or may not apply/help.

R/

Matt

Matthew J. Willis
Living Water Fire Protection, LLC.
1160 McKenzie Rd.
PO Box 877
Cantonment, FL. 32533
850-937-1850 Voice
850-937-1852 Facsimile
[EMAIL PROTECTED]
 

----- >-----Original Message-----
----- >From: [EMAIL PROTECTED] 
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of RFI - Bismarck
----- >Sent: Tuesday, March 18, 2008 8:11 AM
----- >To: [email protected]
----- >Subject: RE: a non-typical type installation question...
----- >
----- >Thanks all!!  Leaning towards a monitored slow-close 
----- >ball valve (Butterball model).  Another nugget of 
----- >knowledge engrained!!  :)
----- >
----- >RFI Chuck
----- >
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Garth W.
----- >Warren
----- >Sent: Monday, March 17, 2008 9:17 PM
----- >To: [email protected]
----- >Subject: Re: a non-typical type installation question...
----- >
----- >I agree, ball valves are not acceptable as a control 
----- >valve.  Butterfly Valves with tampers would work.  If 
----- >you are considering these "floor control valves" 
----- >remember the drain requirements.
----- >
----- >Garth
----- >
----- >----- Original Message -----
----- >From: "Scott A. Futrell" <[EMAIL PROTECTED]>
----- >To: <[email protected]>
----- >Sent: Monday, March 17, 2008 6:58 PM
----- >Subject: RE: a non-typical type installation question...
----- >
----- >
----- >I'm in agreement with Steve regarding supervision.  I 
----- >don't see how you
----- >can install a ball valve.
----- >
----- >>From NFPA 13R:
----- >5.2.12.1.2 Valve Closure Time. Unless the requirements 
----- >of 6.7.1.5 apply,
----- >listed indicating valves shall not close in less than 5 
----- >seconds when
----- >operated at maximum possible speed from the fully open position.
----- >
----- >6.7.1.4 System control or shutoff valves shall be of the 
----- >slow-closing
----- >type unless they meet the requirements of 6.7.1.5.
----- >
----- >6.7.1.5 System control or shutoff valves on backflow 
----- >prevention devices
----- >that are 2 in. (50 mm) or less in nominal size shall not 
----- >be required to
----- >comply with 6.7.1.4.
----- >
----- >Scott Futrell
----- >
----- >(763) 425-1001 Office
----- >(612) 759-5556 Cell
----- >
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Steve
----- >Leyton
----- >Sent: Monday, March 17, 2008 6:30 PM
----- >To: [email protected]
----- >Subject: RE: a non-typical type installation question...
----- >
----- >I guess as a design-only enterprise, we can pull a stunt 
----- >like this here
----- >and there, but I wouldn't concede to that no way no how.
----- >
----- >I agree with Mark, but to underscore even more 
----- >emphatically:  the number
----- >one cause of sprinkler system failure is encumbered 
----- >water supplies and
----- >partially/wholly closed valves account for something 
----- >like 85% of those
----- >instances.   FDNY has lost firefighters in two fires 
----- >that I can remember
----- >in just the past 5 years or so where sectional valves 
----- >buried in walls or
----- >ceilings behind unmarked AP's were left closed and 
----- >allowed sprinklered
----- >structures to become fully involved.
----- >
----- >Ball valves?   Unsupervised?   Nah ...
----- >
----- >Steve Leyton
----- >Protection Design & Consulting
----- >
----- >
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Mark
----- >Sornsin
----- >Sent: Monday, March 17, 2008 4:10 PM
----- >To: [email protected]
----- >Subject: RE: a non-typical type installation question...
----- >
----- >Chuck:
----- >
----- >There should be no problem installing these valves. I 
----- >believe they
----- >should be supervised, as they control water to protected areas.
----- >
----- >The problem with adding sectional valves to a system is 
----- >that they are
----- >easily forgotten. The main cause of sprinkler system 
----- >failure is the shut
----- >valve.  Therefore, as a general rule, one should 
----- >hesitate to add valves
----- >where they are not required.
----- >
----- >But if the owner wants them in place, I would suggest additional
----- >security - especially if they are going to be located in 
----- >a concealed
----- >location (e.g. above a ceiling). Seals or locks seem 
----- >appropriate in
----- >addition to the electrical supervision.
----- >
----- >Mark A. Sornsin, PE
----- >Fire Protection Engineer
----- >Ulteig Engineers, Inc.
----- >Fargo, ND
----- >701.280.8591
----- >[EMAIL PROTECTED]
----- >
----- >
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of RFI -
----- >Bismarck
----- >Sent: Monday, March 17, 2008 5:05 PM
----- >To: [email protected]
----- >Subject: a non-typical type installation question...
----- >
----- >
----- >
----- >Have a fairly small facility (<60 Heads); typical "U" 
----- >shaped building;
----- >the
----- >owner is requesting that prior to going into each "wing" 
----- >a ball valve be
----- >placed to be able to shut down that side of the wing for 
----- >maintenance
----- >purposes...  the AHJ - who also wears the hat as the buildings'
----- >maintenance
----- >super' -was contacted by the owner to request this 
----- >scenario - to which
----- >he
----- >(AHJ) has approved.
----- >
----- >
----- >
----- >Couple questions I have after reading 13R 2007; 
----- >5.2.12.4.4 and 6.7.1.2:
----- >
----- >
----- >
----- >(1)       Acceptable installation then?  (I'm leaning 
----- >towards "yes")
----- >
----- >(2)      Supervised?
----- >
----- >(3)      Non-supervised?
----- >
----- >
----- >
----- >Only reason for #2 & #3 is because they (NFPA sections) don't
----- >'compliment'
----- >one another - yet they don't "contradict" either.  
----- >5.2.12.4.4 states
----- >that
----- >you can use one... doesn't state that it needs to be 
----- >supervised where
----- >6.7.1.2
----- >states otherwise...
----- >
----- >
----- >
----- >Any help or insight would be appreciated!!
----- >
----- >
----- >
----- >RFI Chuck
----- >
----- >
----- >
----- >
----- >
----- >
----- >
----- >
----- >
----- >
----- >
----- >
----- >
----- >
----- >No virus found in this outgoing message.
----- >Checked by AVG.
----- >Version: 7.5.519 / Virus Database: 269.21.7/1332 - Release Date:
----- >3/17/2008
----- >10:48 AM
----- >
----- >
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email 
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)
----- >
----- >
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email 
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)
----- >
----- >No virus found in this incoming message.
----- >Checked by AVG. 
----- >Version: 7.5.519 / Virus Database: 269.21.7/1332 - 
----- >Release Date: 3/17/2008
----- >10:48 AM
----- > 
----- >
----- >No virus found in this outgoing message.
----- >Checked by AVG. 
----- >Version: 7.5.519 / Virus Database: 269.21.7/1332 - 
----- >Release Date: 3/17/2008
----- >10:48 AM
----- > 
----- >
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email 
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to