I agree, ball valves are not acceptable as a control valve.  Butterfly
Valves with tampers would work.  If you are considering these "floor control
valves" remember the drain requirements.

Garth

----- Original Message ----- 
From: "Scott A. Futrell" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Monday, March 17, 2008 6:58 PM
Subject: RE: a non-typical type installation question...


I'm in agreement with Steve regarding supervision.  I don't see how you
can install a ball valve.

>From NFPA 13R:
5.2.12.1.2 Valve Closure Time. Unless the requirements of 6.7.1.5 apply,
listed indicating valves shall not close in less than 5 seconds when
operated at maximum possible speed from the fully open position.

6.7.1.4 System control or shutoff valves shall be of the slow-closing
type unless they meet the requirements of 6.7.1.5.

6.7.1.5 System control or shutoff valves on backflow prevention devices
that are 2 in. (50 mm) or less in nominal size shall not be required to
comply with 6.7.1.4.

Scott Futrell

(763) 425-1001 Office
(612) 759-5556 Cell

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve
Leyton
Sent: Monday, March 17, 2008 6:30 PM
To: [email protected]
Subject: RE: a non-typical type installation question...

I guess as a design-only enterprise, we can pull a stunt like this here
and there, but I wouldn't concede to that no way no how.

I agree with Mark, but to underscore even more emphatically:  the number
one cause of sprinkler system failure is encumbered water supplies and
partially/wholly closed valves account for something like 85% of those
instances.   FDNY has lost firefighters in two fires that I can remember
in just the past 5 years or so where sectional valves buried in walls or
ceilings behind unmarked AP's were left closed and allowed sprinklered
structures to become fully involved.

Ball valves?   Unsupervised?   Nah ...

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mark
Sornsin
Sent: Monday, March 17, 2008 4:10 PM
To: [email protected]
Subject: RE: a non-typical type installation question...

Chuck:

There should be no problem installing these valves. I believe they
should be supervised, as they control water to protected areas.

The problem with adding sectional valves to a system is that they are
easily forgotten. The main cause of sprinkler system failure is the shut
valve.  Therefore, as a general rule, one should hesitate to add valves
where they are not required.

But if the owner wants them in place, I would suggest additional
security - especially if they are going to be located in a concealed
location (e.g. above a ceiling). Seals or locks seem appropriate in
addition to the electrical supervision.

Mark A. Sornsin, PE
Fire Protection Engineer
Ulteig Engineers, Inc.
Fargo, ND
701.280.8591
[EMAIL PROTECTED]


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of RFI -
Bismarck
Sent: Monday, March 17, 2008 5:05 PM
To: [email protected]
Subject: a non-typical type installation question...



Have a fairly small facility (<60 Heads); typical "U" shaped building;
the
owner is requesting that prior to going into each "wing" a ball valve be
placed to be able to shut down that side of the wing for maintenance
purposes...  the AHJ - who also wears the hat as the buildings'
maintenance
super' -was contacted by the owner to request this scenario - to which
he
(AHJ) has approved.



Couple questions I have after reading 13R 2007; 5.2.12.4.4 and 6.7.1.2:



(1)       Acceptable installation then?  (I'm leaning towards "yes")

(2)      Supervised?

(3)      Non-supervised?



Only reason for #2 & #3 is because they (NFPA sections) don't
'compliment'
one another - yet they don't "contradict" either.  5.2.12.4.4 states
that
you can use one... doesn't state that it needs to be supervised where
6.7.1.2
states otherwise...



Any help or insight would be appreciated!!



RFI Chuck














No virus found in this outgoing message.
Checked by AVG.
Version: 7.5.519 / Virus Database: 269.21.7/1332 - Release Date:
3/17/2008
10:48 AM


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to