Hi Pete,
If the system went wet then the pressure switch is activated and the
fire panel should be in full fire. You would not be able to reset the
alarm unless; I believe the system is drained. Also the low air alarm
would keep the panel in trouble. This means if there is a fire the
system would be out of service and not notify anyone in case of fire.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Larrimer,
Peter A
Sent: Wednesday, March 19, 2008 3:08 PM
To: [email protected]
Subject: Dry Pipe Valve going wet

Forum Members:

If a dry pipe valve trips and "goes wet", is there any reason why you
couldn't leave the system piping filled with water assuming that the
weather is not cold enough to freeze it?  I am assuming that the
clappers have been reset externally and that the alarm connections
remain dry since they don't seem to be having problems at this time. 

Why would they want to use an alarm valve in place in liew of just
leaving the dry pipe valve?