On differential dry valves, the surface area of the top of the seat is
several times the water seat dimension.  If a column of water of sufficient
height is allowed to remain on top of this valve, the seat will never raise
and allow a forward flow.
I believe there is something in NFPA that specifically disallows this unless
you are preparing the piping for an internal inspection.

Garth

----- Original Message ----- 
From: "Larrimer, Peter A" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Wednesday, March 19, 2008 3:07 PM
Subject: Dry Pipe Valve going wet


Forum Members:

If a dry pipe valve trips and "goes wet", is there any reason why you
couldn't leave the system piping filled with water assuming that the
weather is not cold enough to freeze it?  I am assuming that the
clappers have been reset externally and that the alarm connections
remain dry since they don't seem to be having problems at this time.

Why would they want to use an alarm valve in place in liew of just
leaving the dry pipe valve?

Thanks in advance.

Peter Larrimer
VA