The clapper would have to be down to close water and pressure on the alarm
switch which normally has no pressure against it.  Plus, the high low switch
(assuming it has one) would be in alarm due to 3-5 times the pressure (with
water as opposed to air) on it.  I don't think the external reset types will
close charged and I know you have to open and reset the traditional style of
dry pipe valve so unless you disable your monitoring switches; the answer is
no.

How's that for long-winded?

Tom
GRS


Hi Pete,
If the system went wet then the pressure switch is activated and the
fire panel should be in full fire. You would not be able to reset the
alarm unless; I believe the system is drained. Also the low air alarm
would keep the panel in trouble. This means if there is a fire the
system would be out of service and not notify anyone in case of fire.


Forum Members:

If a dry pipe valve trips and "goes wet", is there any reason why you
couldn't leave the system piping filled with water assuming that the
weather is not cold enough to freeze it?  I am assuming that the
clappers have been reset externally and that the alarm connections
remain dry since they don't seem to be having problems at this time.

Why would they want to use an alarm valve in place in liew of just
leaving the dry pipe valve?

Thanks in advance.

Peter Larrimer
VA