FYI-- Reliable's DDX valve is can be reset externally as well

Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
     
 
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Charles
Thurston
Sent: Wednesday, March 19, 2008 3:54 PM
To: Larrimer, Peter A
Subject: Re: Dry Pipe Valve going wet

Hello Peter,

See Below

Wednesday, March 19, 2008, 4:07:59 PM, you wrote:

> Forum Members:

> If a dry pipe valve trips and "goes wet", is there any reason why you
> couldn't leave the system piping filled with water assuming that the
> weather is not cold enough to freeze it?

We do this around here some. when a compressor fails or something along
that line. They DO NOT have the capability to trip an alarm system when it
is this way. The pressure port for the Alarm Switch comes off the
intermediate chamber, That does stay wet like this. We "advise" them they
will need to do a Fire Watch while the system is tripped wet.

> I am assuming that the
> clappers have been reset externally and that the alarm connections
> remain dry since they don't seem to be having problems at this time.

Well there is "THAT" word ass-u-ming on a sprinkler forum... From what I
have seen not many dry alarm valve clappers can be reset externally, I
think Victaulic and Tyco have one that can be. I would be willing to
venture a guess the Alarm Line valve is turned off.

> Why would they want to use an alarm valve in place in liew of just
> leaving the dry pipe valve?

> Thanks in advance.

> Peter Larrimer
> VA


> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)



-- 
Best regards,
 Charles Thurston                            mailto:[EMAIL PROTECTED]
  Coastal Fire Protection

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to