Somewhere along the line a collegue said I should write a book about all
this. I responded by saying why, surely it would be categorized as
fiction as the public would never believe it to be true. 

JD 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Thursday, April 03, 2008 8:06 AM
To: [email protected]
Subject: RE: Do you look up?

John,

Much more eloquent than my post. I'm glad to hear it echoed from an AHJ.

Do you have guys with "homebrew spreadsheets" for calc programs, too? 
We have one engineer who wrote his own (According to his promo material,
his expertise is veterinary clinics, but the also does fire
protection) and I seem to end up reviewing a fair amount of his stuff. I
think he has a voodoo doll with a lock of my hair tied to it.

Todd


At 07:12 AM 4/3/2008, you wrote:
>Todd youre dead on, its everyone and heres why.
>
>The property owner who's unreasonable deadlines rush the work
>
>The architect who changes the building layout and doesn't  tell the 
>engineer whos plans were based on an outdated background or whos 
>background is missing details or simply incorrect.
>
>The engineer who shows piping passing through structural members, 
>ductwork, shafts or hoistways, or worse adds a note that the contractor

>shall adjust for field conditions and furnish and install a code
compliant system.
>
>The contractor who bids the job so low theres no room to do the right 
>thing so he or she takes shortcuts to make up that profit that every 
>business must have to stay afloat. Compound that with a tight schedule 
>that the contractor cant keep up with missing milestones before other 
>trades move in ahead of him.
>
>The mechanic who wants to do the right thing but is told to get it done

>period. He or she asks questions but is told to "figure it out that's 
>what I pay you for". Then there are those that could care less about 
>fire protection or simply never been properly trained so its just a 
>paycheck and hell "cant see it from my house."
>
>The ahj whos understaffed, underpaid, undereducated or too proud to ask

>questions. Deadlines are deadlines and city hall demands answers 
>especially when property owners right or wrong start making phone 
>calls. The ahj is the collection point for all of the above.
>
>But the ahj can make a difference by establishing a no nonsense policy 
>from the beginning where plans on napkins and hydraulic calculations 
>using homebrew spreadsheets wouldn't be accepted. The AHJ can set that 
>policy at the beginning such that no permit is issued until things are 
>right and field change documentation is expected prior to or at the 
>time of the hydro. The AHJ can do this such that the message travels up

>through the chain of command before a project starts and not after its 
>gone beyond the point of no return.
>
>In the end its not about fire protection but rather management.
>
>John Drucker
>Fire Protection Subcode Official (AHJ)
>Former Senior Project Manager, WTC, NYC 1993-2001
>
>
>
>
>
>-----Original Message-----
>From: [EMAIL PROTECTED]
>[mailto:[EMAIL PROTECTED] On Behalf Of Todd 
>Williams
>- FPDC
>Sent: Thursday, April 03, 2008 5:37 AM
>To: [email protected]
>Subject: RE: Do you look up?
>
>The complaint here is not about the engineering, but the installation. 
>We are talking about what is physically in the building. You're a PE, 
>Jeff; how many times has an installer changed your drawings? My guess 
>is a lot. I know in my situation, I am rarely asked to certify an 
>installation once it is complete. I don't hold up anybody's money and I

>don't hold up the CO. Then the last eyes for seeing the job was done 
>right is the AHJ. If it is not caught there, that's how it remains. The

>fault may well be with the specifying engineer (if there is one), but 
>it may lie elsewhere.
>
>
>At 10:07 PM 4/2/2008, you wrote:
> >Sorry for the late reply to Mark's comments, I've been travelling all
day.
> >
> >   I saw this and felt compelled to repeat my previous thoughts on 
> > this issue.  Mark's comments bring me to a statement that I have 
> > made on here before, and I will likely again, the next time this
comes up.
> >
> >   You cannot just complain about this PE issue.  Turn them in!!  
> > There is no other way.  Their regulating Boards can do nothing 
> > without a complaint, and for that matter thay will NOT even know 
> > about it, unless WE speak up and do something about it.
> >
> >   Yes, that's right, an engineer telling you to turn in a fellow 
> > engineer.  I will not defend anyone that claims this or anything 
> > else as an area of expertise when they are not actually qualified.
> >
> >   Turn them in!  And don't get fed up if nothing happens right away.

> > Their investigations may take a while.
> >
> >   Again, rather than seeing all of these complaints about inept 
> > specifying engineers, let's all do something different now, or it 
> > will only get worse.
> >
> >   Gather your facts, file the complaint, and turn them in.
> >
> >
> >   Jeff Hewitt, PE, SET, MSFPE (Professional Member)
> >   Corporate Engineer
> >   Bi-State Fire Protection Corporation
> >   St. Charles, MO  63301
> >
> >Mark Sornsin <[EMAIL PROTECTED]> wrote:
> >   When I "look up" at work that is incorrect, I always wonder if 
> >there was an engineer of record involved on the project. Then I 
> >wonder how much money they were paid to be the "engineer of record." 
> >Then I wonder how much time they actually spent on their "performance

> >spec" that included no performance criteria outside of references to
code.
> >
> >Obviously, mine is a cynical perspective of my colleagues in the 
> >engineering world. I certainly understand the reality that there 
> >aren't enough skilled engineers to be involved on all sprinkler 
> >projects. To say the typical "performance spec" is criminal may be 
> >excessive (maybe they couldn't get enough fee to do the project 
> >justice...?) But I do know that all engineers who rely on their 
> >blanket statement about systems "meeting code" (but don't have the 
> >ability to verify compliance) to are teed-up nicely to lose the 
> >litigation battle should a fire ever occur. As Chris has reminded us,

> >there seem to be an inordinate number of screwed up systems out 
> >there, so it's really a wonder why more engineers aren't brought to 
> >task through litigation. Sometime I wonder if it is because of the 
> >ironic fact that "everyone" knows the mechanical engineer is not the 
> >expert - it's the sprinkler contractor. So engineers are forgotten
when problems arise...???
> >
> >Don't mean to tangent into another PE-bashing thread, but it just 
> >peeves me that there are "professionals" getting paid for being lazy
fools.
> >
> >Mark A. Sornsin, PE
> >Fire Protection Engineer
> >Ulteig Engineers, Inc.
> >Fargo, ND
> >701.280.8591
> >[EMAIL PROTECTED]
> >
> >
> >-----Original Message-----
> >From: [EMAIL PROTECTED]
> >[mailto:[EMAIL PROTECTED] On Behalf Of Chris 
> >Cahill
> >Sent: Wednesday, April 02, 2008 12:29 PM
> >To: [email protected]
> >Subject: Do you look up?
> >
> >I imagine, like me, you all (ya'll for some of you) on the very rare 
> >occasions you are not working look around at sprinkler systems where 
> >you live, shop and play.
> >
> >
> >
> >It's a very rare occasion I don't see something that appears
deficient.
> >For
> >example, in a grocery store the one head on the back side of the main

> >is missing over HPS and a mess of piping creating a ceiling without 
> >heads under them, at a Home Depot 190 psi on the wet side of an 
> >auxiliary dry valve, or the local high school with sidewall heads 
> >about 15-20' down from the peak of the very large skylight. This is 
> >all in the last two days as an example but see similar all the time.
> >
> >
> >
> >The sad part is I'm not really trying. What if I had the plans and 
> >calcs, how much more would there be? Or really looked at the whole 
> >building instead of a casual look at where I happen to be? Or the 
> >scary part what if I actually considered the hazard vs. the design?
> >
> >
> >
> >I also realize two issues - most times what I see probably won't 
> >cause the system to fail in a fire IF that is the only thing wrong. 
> >There is a "probably" and an "if " in the last sentence which means 
> >there are cases that will fail, just not many IMHO. And second we 
> >make mistakes too.
> >
> >
> >
> >The heads at the peak - just because an AHJ didn't call it a 
> >deficiency doesn't mean it's OK. Certainly it is possible there is a 
> >documented and proactively approved alternate method out there on 
> >this but I strongly doubt it. Now I'm sure the missing head has a 
> >perfectly rational explanation of how it got like that. The W.O. is 
> >there and it must be plugged or the system is off. It's not a TI 
> >thing long after the original construction; this is a very new 
> >building. Can't rationalize how you get 190 psi by accident or 
> >approval.
> >
> >
> >
> >MN is more regulated than most (but not all) areas. Do you see this 
> >stuff too? What if anything can you really do about it?
> >
> >
> >
> >Chris Cahill, P.E.
> >
> >Fire Protection Engineer
> >
> >Sentry Fire Protection, Inc.
> >
> >
> >
> >763-658-4483
> >
> >763-658-4921 fax
> >
> >
> >
> >Email: [EMAIL PROTECTED]
> >
> >
> >
> >Mail: P.O. Box 69
> >
> >Waverly, MN 55390
> >
> >
> >
> >Location: 4439 Hwy 12 SW
> >
> >Waverly, MN 55390
> >
> >
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >To Unsubscribe, send an email
> >to:[EMAIL PROTECTED]
> >(Put the word unsubscribe in the subject field) 
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >To Unsubscribe, send an email 
> >to:[EMAIL PROTECTED]
> >(Put the word unsubscribe in the subject field)
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >To Unsubscribe, send an email 
> >to:[EMAIL PROTECTED]
> >(Put the word unsubscribe in the subject field)
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, Connecticut
>www.fpdc.com
>860.535.2080
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email 
>to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email 
>to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to